ghc



Joined: 15/06/07
Posts: 83
Well, yeah, again, electric shocks from mics !!
      #576976 - 06/02/08 06:21 AM
Hi everyone !!
Ok, if you are interested(and it is, i'm advising to read through it, plenty of good info) i've posted this discussion before on 24/08/07 ''Electric shock from mic while touching guitar, ......''
I just came across the same problem a while ago, last week !!
My mixer was plugged in to a socket in the wall, so as musicians, but spread in different corners, different sockets (all on the walls).
And, to stop the mic from being electically charged, all i had to do was: Plug out my mixer which was going to a socket in the wall, and in the same socket (on the wall) i plugged in an extention lead, and then i plugged in the mixer in the extention+vocalists guitar ?!
Sounds strange to me but it worked !!
Could anyone explain to me (and to all of us) why did it work ?!
I just can't understand it !! Lost !!
Thanks guys !!

--------------------
Don't blame the world
Find a solution !!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577000 - 06/02/08 09:24 AM
Assuming the guitar amp was properly earthed, then by plugging the guitar amp into the same mains extension as the mixer, you ensured their earths were at the same potential, and thus no shocks.

I suspect the socket that the guitarist was using originally had no earth, or a very poor earth.

There really is no excuse these days for not checking each and every mains socket used in every venue with a simple socket tester to make sure they are wired correctly and are safe to use.

It is also a much better idea to run everything from the same socket or adjacent sockets, to reduce the risk.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577025 - 06/02/08 10:07 AM
Call me extremely pedantic...

It's very rare that a mic will ever give you an electric shock. It's almost always the fault of the guitar / amp; it's only by touching the earthed mic that this becomes apparent. It always winds me up when people blame the mics rather than the true cause...

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Paul Soundscape



Joined: 27/06/06
Posts: 722
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577029 - 06/02/08 10:10 AM
i dont think it has anything to do with the amp.
i played at the colston hall in bristol and i even had problems there, and my equipment is certainly earthed!
It was that our amps were plugged in to a different circuit to the mixing desk

--------------------
Live Sound and Studio Engineer


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Paul Soundscape]
      #577042 - 06/02/08 10:41 AM
Quote Paul Supersonix Studios:

i dont think it has anything to do with the amp.




To be fair, it is most usually a problem associated with a disconnected earth on guitar amps (to kill the hum, man!).

Quote:

my equipment is certainly earthed!




I'm glad to hear it, but can you be as certain that the socket you plugged it into is properly earthed, or that the equipment, sockets, mains cables and plugboards that everyone else uses are properly earthed?

The only way to be sure and safe is to test the mains sockets you plan to use before using them, and check that everyone's equipment is earthed correctly before allowing them to plug anything in.

Quote:

It was that our amps were plugged in to a different circuit to the mixing desk




Then there was a potentially lethal fault somewhere in that building. The difference in earth potential between sockets should be no more than a volt or two at most. To feel a shock when touching an earthed mic suggests that an earth was missing from the singing guitarist's rig. If that's the case, then he is playing on borrowed time....

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Paul Soundscape



Joined: 27/06/06
Posts: 722
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577102 - 06/02/08 12:57 PM
yeah well as hundreds of professional touring chart topping artists play there every year you would have thought that it would be properly earthed? maybe not,
the reason i said it wasn't the guitar amp was because i was getting shocks(and i play bass and sing) and so was our guitarist(who also sings) and its never happened before?

Edited by Paul Supersonix Studios (06/02/08 12:59 PM)


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Paul Soundscape]
      #577112 - 06/02/08 01:24 PM
Quote Paul Supersonix Studios:

yeah well as hundreds of professional touring chart topping artists play there every year you would have thought that it would be properly earthed? maybe not,




The first rule of not dying is to not make assumptions like that. Faults happen. Things can change. When we rigged for some SOS seminars at the old Wembley Arena site, I found four faulty sockets in the same conference room -- a room that was used everyday by all and sundry. One socket had no earth, two were live-neutral reversed, and one just had no power. It happens! Often, the screws clamping the cables inside work lose or tarniosh and oxidise. Sometimes they weren't done up tight in the firtst place, and as the cable oxidises the connection goes high-resistance. That's all that's needed to make the safety earth next to useless! Sometimes someone else has had a major fault and the cable or the socket has been damaged but not reported to be fixed. Hence my advice to check them before using them.

Quote:

the reason i said it wasn't the guitar amp was because i was getting shocks(and i play bass and sing) and so was our guitarist(who also sings) and its never happened before?




Were both your amps plugged into the same mains extension plug board by any chance? Or the same wall socket? If so, you've probably just identified where the missing earth was.

Clearly, there was a serious and potentially fatal fault somewhere. It could have been the earths protecting the sound desk, or it could have been the earths protecting the guitar and bass amps.

In my experience, shocks when touching a microphone are almost always because the mic body is properly earthed but the guitar amp's earth is disconnected, so that the 'earthed' metalwork on the amp (and guitar string earthing) floats up to half mains voltage (115V).

You won't feel that while playing as long as you don't touch anything else earthed, but the moment you do, you'll get the shock.

Now the missing earth might not be because the safety earths in the amps have been deliberately disconnected -- it could just as easily be because a mains cable or extension board has been damaged, or the wall socket could be faulty, as I've explaiend.

It's a less common scenario, but certainly still one worth investigating, that it could equally have been the other way around -- the guitar amps were properly earthed and it as the mixing console earth that was at fault. In that case, the mic's body would have floated to 115V, but you would have got the same tingle effect through the grounded strings.

Sadly, without all the same equipment set up in the same room in the same way, we'll only ever be guessing what the actual problem was. But it would be foolish to dismiss it and not check everything you can carefully.

As I said, the location of that discontinuous earth (or earths -- there could be more than one fault here) could be at any of a variety of places. The wall sockets, the extension cables, the mains plugs, the mains cables, the pluig-boards, or inside the equipment itself. The only way to be sure is to check every single mains cable you used, every extension cable, and every piece of equipment.

In fact, this really is something you should do regularly anyway. Cables get snagged and cut, or tripped over pulling the wires from the plugs, and screw connections inside plugs can work loose and wires corrode and oxidise.

If they all check out okay, then it was probably the mains sockets in the venue -- it really isn't that uncommon! Buy a tester, and make a point of using it next time. it only take a few seconds. Also, to be almost completely safe, make sure you run all your own equipment through an RCD, and persaude all the others in the band (and FOH) to use RCDs too.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Paul Soundscape



Joined: 27/06/06
Posts: 722
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577136 - 06/02/08 02:14 PM
ok thanks hugh that makes a bit more sense now, it was a while ago so cant exactly remember where we were plugged in to but yeah i always use RCD's now.

it only happened when we sang and touched our strings.
Cheers

Edited by Paul Supersonix Studios (06/02/08 02:15 PM)


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Paul Soundscape]
      #577177 - 06/02/08 03:47 PM
Quote Paul Supersonix Studios:

it only happened when we sang and touched our strings.




Yes, it would.

Normally, the strings are earthed through the guitar cable's screen to the guitar amp, and from their to the mains safety earth of the amp's mains lead.

The mic body is earthed through the mic cable screen to the mixer, and from there to the mains safety earth of the mixer's mains lead.

If one or other of those mains safety earths becomes high resistance or disconnected, then the mains input filtering of the amp or mixer will tend to pull everything connected to the now disconnected earth line up to half mains volts (115V in the UK and Europe).

If you are playing the guitar while touching the mic body as you sing, you complete a circuit, one side of which is earthed, and the other is sitting at 115V. it doesn't matter which way around it is -- which side is still earthed and which is floating -- the results ae the same.

If you're lucky it will just tingle unpleasantly. If you're unlucky there'll be a bang and the gig will come to a premature end... as will the person who formed the link in the circuit.

You said this only affected you and the guitarist, and that's often the case. Vocalists generally only touch the mic and nothing else -- so there is no circuit. Likewise keyboard players generally only touch plastic keys, so there's still no circuit.

The worst case scenario is when the circuit is formed across the hands -- one hand on the guitar strings, the other on the mic. That way any current flow is straight across the chest, through the heart, and is likely to stop the heart. One ex guitarist...

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
jamaicanDave



Joined: 24/01/08
Posts: 28
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577224 - 06/02/08 04:41 PM
never happened to me b 4 but thanx 4 posting that thread...
it's gonna save me loads of time in the future...cause i'm sure it'll happen


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: Paul Soundscape]
      #577282 - 06/02/08 06:40 PM
Quote Paul Supersonix Studios:


i played at the colston hall in bristol and i even had problems there, and my equipment is certainly earthed!
It was that our amps were plugged in to a different circuit to the mixing desk




I could tell you a few stories about that venue, but probably had better not.

Most touring acts will plug distro into the heavy stage power tie stage right (good for 400A or so IIRC) and forgo the use of the random 13A points except for back stage tea and coffee.

That the earthing is a little suspect comes as no surprise (No reflection on the house crew, council run venue and Bristol council, well 'nuff said).

I would heavily advocate always testing before you plug in anywhere, in any venue and that the use of RCD protection on backline supplies is just good sense (along with FOH if you don't trust things).

Note that most simple socket testers cannot identify a neutral/earth reverse.

There are a scary number of dodgy sockets out there, test everything and be paranoid, it's good for you.

Incidentally, IME CEE form sockets are less likely to be miswired as people pay more attention to the 'industrial' power then they do to the domestic stuff (Good reason to use them if available).

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Paul Soundscape



Joined: 27/06/06
Posts: 722
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577296 - 06/02/08 07:14 PM
the engineer was a right pr*ck he just said "deal with it". in the end our guitarist just got so annoyed at the end of the set just smashed over the mic stand lol

--------------------
Live Sound and Studio Engineer


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
DingoDave



Joined: 05/02/08
Posts: 79
Loc: Cardiff
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577356 - 06/02/08 09:36 PM
Hehe my guitarist was getting static off his guitar in band practice dont know why it happend, he was also using a mic at the time and quite close to the amp and socket. It was amusing to watch when now and again hed jump in the middle of a song with a small yelp!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Paul Soundscape



Joined: 27/06/06
Posts: 722
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577368 - 06/02/08 10:06 PM
haha yeah its not fun if your being shocked after a 30 minute set my mouth was burning.

--------------------
Live Sound and Studio Engineer


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Paul Soundscape]
      #577418 - 07/02/08 01:18 AM
Quote Paul Supersonix Studios:

the engineer was a right pr*ck he just said "deal with it". in the end our guitarist just got so annoyed at the end of the set just smashed over the mic stand lol




You are completely within your right to walk out there.

NOTHING is worth the risk you just put yourself through(30 minutes???!!!!). If they have a problem with you walking out, tell them you will feel happy to have the local inspector come in and make sure the building is up to code and if that is the case you will come back. But until then something is very much NOT right there and they are endangering lives like that. Honestly the engineer that says, deal with it, to something like that needs to be fired on the spot. Maybe then he will learn not to screw with electrocuting people.

Seablade

NOTE: I am in the US, though I would imagine a similar safety inspection exists in the EU for such situations.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577428 - 07/02/08 01:44 AM
City council venue Seablade, the place (a ~1,800 seat somewhat run down neoclassical pile last time I was there) is owned by the AHJ! I understand that they have done some work on it in the interim, but the real plan for as long as I can remember has been to replace it.

This is the council which owns another venue where you always had to ensure a lantern was plugged into the first socket on the FOH bar and securely clamped to the bar as that was the only one with the earth connected (Lots of moaning from us, zero action from the council, and this is in 240/415V land)! Mind you, they also supplied me a 'street lighting technician' to fill a rider requiring the venue to provide a 'lighting technician', nice guy, but about as useful as a chocolate fireguard.

I do wonder if that 'engineer' was actually a hired in PA company as I don't recall that place having any PA worthy of the name (And from what I recall of working there a few times, that does not sound like behaviour the resident chief would have accepted from his people).

It does however sound like the sort of thing a pissed off third party sound provider might perpetrate after a bad day.

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: DingoDave]
      #577435 - 07/02/08 02:05 AM
Quote DingoDave:

Hehe my guitarist was getting static off his guitar in band practice dont know why it happend




Not being funny here, mate, but you are dismissing a seriously life-threatening situation here. You need to find out why it happened. Something is UNSAFE in your rig.

Quote:

It was amusing to watch when now and again hed jump in the middle of a song with a small yelp!




I wonder how many people will laugh when your mate -- OR YOU -- DIE!

This is serious and it happens everyday. And if something nasty does happen, and it can be shown that you were aware of the fault but did nothing to rectify the problem, it won't do you much good either!

Seriously -- sort this out NOW. Get the gear checked. Get the room wiring checked.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Matt P
member


Joined: 19/06/04
Posts: 348
Loc: Manchester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577444 - 07/02/08 02:45 AM
I know it's been said a million times before, but surely we can all agree that this topic warrants being made a sticky.

Also, Dan/Hugh/anyone, do you have a particular socket tester that you recommend? I know for a fact that my rather basic Maplins jobby (the name of which completely escapes me) will spot a disconnected earth, but won't pick up on a reversed live/neutral. Dan, I think I've heard you talk about stuff Martindale(?) before now?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: dmills]
      #577457 - 07/02/08 06:13 AM
Quote dmills:

City council venue Seablade, the place (a ~1,800 seat somewhat run down neoclassical pile last time I was there) is owned by the AHJ! I understand that they have done some work on it in the interim, but the real plan for as long as I can remember has been to replace it.

This is the council which owns another venue where you always had to ensure a lantern was plugged into the first socket on the FOH bar and securely clamped to the bar as that was the only one with the earth connected (Lots of moaning from us, zero action from the council, and this is in 240/415V land)! Mind you, they also supplied me a 'street lighting technician' to fill a rider requiring the venue to provide a 'lighting technician', nice guy, but about as useful as a chocolate fireguard.

I do wonder if that 'engineer' was actually a hired in PA company as I don't recall that place having any PA worthy of the name (And from what I recall of working there a few times, that does not sound like behaviour the resident chief would have accepted from his people).

It does however sound like the sort of thing a pissed off third party sound provider might perpetrate after a bad day.

Regards, Dan.




Again, yank over here sadly, but I would say then the next step is to take it over the city. At least in the US this would violate NATIONAL safety standards, so there is nothing stopping someone above the city from shutting it down if need be. Again I would venture a guess in the EU that a similar situation exists.

I know it sucks, but honestly they need to be forced to do something. This is waiting for someone to die as described right now. No hyperbole at all, it literally is a matter of waiting till the first person dies before anything is done unless someone goes over their heads if the city is unwilling to do anything with it.

Honestly, there have been venues I have told production companies never to book again as they were dangerous along this level. This would certainly qualify, step one is to never play it again, and make sure noone you know plays it until they get this fixed. Step 2 would be to report it over the heads of the city IMO.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Matt P]
      #577458 - 07/02/08 06:15 AM
Quote Matt P:

I know it's been said a million times before, but surely we can all agree that this topic warrants being made a sticky.




Yea at this rate, I gotta agree, something needs to be done to keep this perfectly visible, not sure if a sticky thread is the right answer or not. Maybe an FAQ section along the lines of Martin's computer FAQs? Ah well up for the mods/admins to decide not me.

Anyways to answer your other question I bought this kit for basic electrical analysis that I carry with me.

http://www.lowes.com/lowes/lkn?action=productDetail&productId=205783-7 2068-TK-30&lpage=none

I believe the socket tester in it wil check for a live/neutral reverse, but I will double check tomorrow. At the moment I need to get some sleep and don't feel like getting dressed to go out to the car to check.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: seablade]
      #577544 - 07/02/08 10:44 AM
when i have this problem i use a multimeter and the odd radiator to find which earth is bad and then i put a sticker on it saying "Faulty. This is not to be used until repaired" then i tell the venue management what i've done and suggest that it's repaired. If i'm feeling really bolshy i'll follow it up and report them to the local coucil, their licensing authority or HSE if the sticker was removed without being rectified (i have done this to a council venue whose 63Amp supply was LN reversed).

if you knew what you were doing and if you had the appropriate test gear, you could measure between the earth connections on the stage and mixer supply sockets and see if there is a voltage -more than 5 volts or so suggests a possible problem, double figures means a definite issue with earthing in the building. i have found over a 120 volts on an earth in a leisure complex venue.

a missing or dodgy earth is potentially lethal should a fault condition occur, and the venue would be fined heavily or shut down once HSE had been in there should there be an accident (happened to a franchise of a food chain in my home town after a lethal shock).

also any venue needs an annual electrical inpection to get their PEL, so it would be good to ask for a copy of the report for this "council-run" venue -i think as a council they are obliged to supply one to a formal request. stir up some mud, you might get things to happen before someone dies.

that aside, the usual reason for shocks on microphones is a removed earth on guitar amp plugs -in this case it could be a bad earth from either side from the mains sockets.

anybody who lives in Bristol fancy verifying this? it does sound like something does need to be done.

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
feline1
active member


Joined: 23/06/03
Posts: 3651
Loc: Brighton, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577551 - 07/02/08 10:56 AM
Thanks to previous SoS threads on this, I now always bring my 'Martindale socket tester' to everygig,
and fit a couple of Wickes RCDs onto the bands' gear.

Occasionally they trip out in the middle of songs, so the band can be a little "auch! not that bloody thing that ruins our gigs!" but I just keep reminding them that leaving the stage in an ambulance would ruin the gig even more.

--------------------
~~~ A weasel hath not such a deal of spleen as you are tossed with! www.feline1.co.uk ~~~


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: feline1]
      #577563 - 07/02/08 11:12 AM
find an electrician friend to measure your gears leakage current feline -most PAT testing gear will do this -see if you have some borderline equipment or if you have any congealed beer in any of your socket strips...

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Paul Soundscape



Joined: 27/06/06
Posts: 722
Re: Well, yeah, again, electric shocks from mics !! new [Re: Nathan]
      #577571 - 07/02/08 11:23 AM
Quote:

I do wonder if that 'engineer' was actually a hired in PA company as I don't recall that place having any PA worthy of the name (And from what I recall of working there a few times, that does not sound like behaviour the resident chief would have accepted from his people).




nah it was the inhouse lampy i think. they have some sort of turbosound rig in there, not very good though.

--------------------
Live Sound and Studio Engineer


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
feline1
active member


Joined: 23/06/03
Posts: 3651
Loc: Brighton, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: Nathan]
      #577589 - 07/02/08 11:59 AM
Quote Nathan:

find an electrician friend to measure your gears leakage current feline -most PAT testing gear will do this -see if you have some borderline equipment or if you have any congealed beer in any of your socket strips...





nah, the time it tripped, there was spilt beer about an inch deep all over the stage and the 4-ways, so "go figure", etc etc...

--------------------
~~~ A weasel hath not such a deal of spleen as you are tossed with! www.feline1.co.uk ~~~


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: feline1]
      #577590 - 07/02/08 12:01 PM
heh, no argument

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
chris...
active member


Joined: 12/03/03
Posts: 4152
Loc: Glasgow
Re: Well, yeah, again, electric shocks from mics !! new [Re: Nathan]
      #577887 - 08/02/08 01:07 AM
Quote Nathan:

also any venue needs an annual electrical inpection to get their PEL, so it would be good to ask for a copy of the report for this "council-run" venue -i think as a council they are obliged to supply one to a formal request




Yep - with very few exceptions, under Freedom of Information they are required to supply any document held by the public authority.

The request for information must be somehow written down (email considered fine) but technically doesn't have to be in any way "formal".

You don't have to live in bristol - anyone should be able to email: foi at bristol.gov.uk and ask for a copy of the report....


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577962 - 08/02/08 10:16 AM
As this is a topic that comes up regularly, and is 'mission critical' I have made it a sticky as suggested.

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
The muso



Joined: 11/12/07
Posts: 131
Loc: Scotland
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #577963 - 08/02/08 10:19 AM
Quote Hugh Robjohns:

As this is a topic that omes up regularly, and is 'mission critical' I have made it a sticky as suggested.

hugh



Applause!
Righto, is there prize for writing the best definitive Electrical Safety guide?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
PeteJ



Joined: 13/08/06
Posts: 84
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577987 - 08/02/08 11:05 AM
Hi all,
At the weekend I was getting small shocks from the main vocal mic (our singer doesn't play any instruments or have anything plugged into mains). There was no unecessary phantom power and the problem was only on the main vocal. I was splitting it into 2 channels and using 1 to drive monitors... could it have been something in the desk? Anyone got any ideas how this can be fixed if i encounter it again?
Cheers
Pete


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sylle



Joined: 08/02/08
Posts: 2
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #577991 - 08/02/08 11:14 AM
Tried to search in this thread about it, but i was surprised to see that noone came with the suggestion to put a DI between the amp and the guitar to prevent shocks.
Of course you have to plug the DI into the mixer or remotebox on the stage, just to even out the differences in current between different outlets. But with that done, you won't have any problem with shocks while grabbing your guitar and singing.

Best regards
Sylvester


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
mpostor
member


Joined: 04/09/03
Posts: 409
Loc: S.W. London
Re: Well, yeah, again, electric shocks from mics !! new [Re: Sylle]
      #578064 - 08/02/08 01:39 PM
That won't fix any problems with earthing on the mains sockets, though...

You could still injure/kill yourself.

Although, on the bright side, that annoying hum will have been stopped...



Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #578120 - 08/02/08 03:29 PM
Dodgy socket wiring would be my bet for the shocks from the (non guitarist) vocal mic.
Get a simple three lamp socket tester, and use it every time, you will find some amazing things.

On the subject of guitars, I have one that has had a low value class Y cap added in series with the lead that connects the bridge to the screen.
It has little effect on the screening, but means that the path to the amp will be too high impedance to deliver a belt that is likely to be fatal (Cheap insurance, and I commend this modification to the house).

Not of course that this makes lifting the safety ground safe, but it does provide some protection against muppetry.

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
The muso



Joined: 11/12/07
Posts: 131
Loc: Scotland
Re: Well, yeah, again, electric shocks from mics !! new [Re: dmills]
      #578133 - 08/02/08 03:54 PM
Quote dmills:



Not of course that this makes lifting the safety ground safe, but it does provide some protection against muppetry.

Regards, Dan.




LOL.
Good one.
Should be in 'Top Tips'.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
PeteJ



Joined: 13/08/06
Posts: 84
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #578176 - 08/02/08 05:15 PM
Cheers Dan,
I'm not totally sure what you mean by the socket tester.. the only power she could have been connected to was from FOH.. on it's own feed from the distro... maybe test that output? I don't get how we didn't encounter the same problem with other (vocal) mics.
Cheers
Pete


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: PeteJ]
      #578178 - 08/02/08 05:25 PM
Quote PeteJ:

At the weekend I was getting small shocks from the main vocal mic (our singer doesn't play any instruments or have anything plugged into mains).




By small shocks, do you mean static 'zaps' -- short, sharp zaps that are not continuous -- or do you mean half mains voltage continuous electric shocks?

The former is caused by clothing or flooring, generally and isn't lethal but can be startling. The latter is potentially lethal...

I'm ubnclear when you say you got shocks but the singer doesn't play anything. Was the singer getting shocks too?

Quote:

There was no unecessary phantom power




Phantom power is DC and low voltage, so it's not a factor in this.

Quote:

and the problem was only on the main vocal.




That is very odd... and quite unlikely if it is real faulty-earth style electric shocks! But could be possible if it was static shocks.

Quote:

I was splitting it into 2 channels and using 1 to drive monitors... could it have been something in the desk?




Do you mean two channels of the same desk, or split to two different desks?

Quote:

Anyone got any ideas how this can be fixed if i encounter it again?




Check all the mains earths on all the equipment, mains leads, and distro boards. Check the wall sockets at the venue before using them. And power eveything via RCDs.

hugh


--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
PeteJ



Joined: 13/08/06
Posts: 84
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #578227 - 08/02/08 07:23 PM
Thanks Hugh...
Static shocks I reckon. Sorry about the confusing bits.. I just mix the band so when I said myself and the singer it was me during soundcheck and her during the show. Maybe it was floor / clothing related.. I'll check out what she's wearing next time. Any other ways of minimizing this? Changing cables / stands / mics?
The channel thing was just that I had to mix mons + foh from the same board so I y-split the main vocal into 2 channels of the same desk - then used one for out-front and one to send to monitors with different eq.
Thanks for your help..
best
Pete


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: PeteJ]
      #578382 - 09/02/08 10:48 AM
Quote PeteJ:

Static shocks I reckon.




Yes, sounds more likely.

Quote:

I'll check out what she's wearing next time. Any other ways of minimizing this?




Can't do anything with the mics/stands etc. They have to be earthed for safety. Best to check your lady singer for static-inducing underwear before every gig

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
The muso



Joined: 11/12/07
Posts: 131
Loc: Scotland
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #578391 - 09/02/08 11:19 AM
Quote Hugh Robjohns:

Best to check your lady singer for static-inducing underwear before every gig

hugh



You could always attach some of those static tails you used to see under the rear bumpers of cars in the 80's.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
hifistud2



Joined: 12/02/06
Posts: 795
Loc: Near Sunderland, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #578412 - 09/02/08 12:31 PM
Quote:

Best to check your lady singer for static-inducing underwear before every gig




Something I've made a point of for years. Sometimes a visual check alone is not enough, as you're doubtless well aware. However, no matter how the check is carried out, I find the best option is to ensure it's removed, and held in safe keeping pending further investigation.

--------------------
[url=http://www.facebook.com/pages/hifi-studios/117322741632389[/url]


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Grim Audière



Joined: 02/09/04
Posts: 375
Loc: UK and France
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #578498 - 09/02/08 05:06 PM
The HS executive do a leaflet on electrical safety for entertainers. You can download it here as PDF file:

HSE executive PDF on electrical safety for entertainers

Note sure it adds much to the discussion, but it's a useful reminder.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
PeteJ



Joined: 13/08/06
Posts: 84
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #579035 - 11/02/08 10:57 AM
Thanks all
Turns out she had three layers of nylon on under that dress!... hang on... make that four


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: PeteJ]
      #579046 - 11/02/08 11:24 AM
valentine's day is coming... buy her some silk!

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #579090 - 11/02/08 12:51 PM
Off Topic, Off Topic ...pheeeeep!



--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
hifistud2



Joined: 12/02/06
Posts: 795
Loc: Near Sunderland, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: PeteJ]
      #579141 - 11/02/08 02:11 PM
Yerst... it all needs takihng off...

one layer at a time...

slowly...


video please!!!!

--------------------
[url=http://www.facebook.com/pages/hifi-studios/117322741632389[/url]


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
The muso



Joined: 11/12/07
Posts: 131
Loc: Scotland
Re: Well, yeah, again, electric shocks from mics !! new [Re: Grim Audière]
      #579178 - 11/02/08 03:14 PM
Quote Grim Audière:

The HS executive do a leaflet on electrical safety for entertainers. You can download it here as PDF file:

HSE executive PDF on electrical safety for entertainers

Note sure it adds much to the discussion, but it's a useful reminder.




Good man.
Definately ON topic!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: seablade]
      #579186 - 11/02/08 03:28 PM
Quote seablade:

Quote Matt P:

I know it's been said a million times before, but surely we can all agree that this topic warrants being made a sticky.




Yea at this rate, I gotta agree, something needs to be done to keep this perfectly visible, not sure if a sticky thread is the right answer or not. Maybe an FAQ section along the lines of Martin's computer FAQs? Ah well up for the mods/admins to decide not me.

Anyways to answer your other question I bought this kit for basic electrical analysis that I carry with me.

http://www.lowes.com/lowes/lkn?action=productDetail&productId=205783-7 2068-TK-30&lpage=none

I believe the socket tester in it wil check for a live/neutral reverse, but I will double check tomorrow. At the moment I need to get some sleep and don't feel like getting dressed to go out to the car to check.

Seablade




For the record, yes mine does do a Hot/Neutral Reverse check. Cheap 20 buck kit got me a cheap multimeter, a socket tester, and voltage detector, not a bad deal to me.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
The muso



Joined: 11/12/07
Posts: 131
Loc: Scotland
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #579202 - 11/02/08 04:11 PM
Good link here;

http://professional-sound.com/soundadvice/datadirectory/viewnews.cgi?id=11 91436814


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Dale Campbell



Joined: 10/10/04
Posts: 528
Loc: Cheltenham
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #579320 - 11/02/08 08:29 PM
I really do love my wireless setup as it puts several feet of air between me and electrocution

--------------------
Crazy guitar beating - www.myspace.com/dalecampbell


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Dale Campbell]
      #579511 - 12/02/08 10:58 AM
There is something to be said for that...

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Stewart Newlands



Joined: 27/03/08
Posts: 11
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #596316 - 27/03/08 07:55 PM
For the new BS7909 code of practice (in draft now) it is recommended that (for small systems from 13A outlets etc) you check the sockets using at least a socket test device that includes an Earth loop indicator and you should not use any socket that has an earth loop above 500 ohms, something like this http://www.martindale-electric.co.uk/sockets.htm#ez150

You should also have an RCD, and you may need to bring this with you as some places still do not have them fitted.
see also the HSE publications: INDG247 - Electrical safety for entertainers http://www.hse.gov.uk/pubns/indg247.pdf
and GS50 Electrical safety at places of entertainment which is is for the venue.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
revbobuk



Joined: 31/12/06
Posts: 4
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #598387 - 01/04/08 05:22 PM
Now (referring to a post up the page a bit, where Hugh seemed to be suggesting that mics and stands are earthed for safety reasons) that would be a first for me - did you really mean that mic. stands should/must be earthed? I don't think I've ever seen that. Mics, yes. But stands? How would you do that?

Edited by revbobuk (01/04/08 05:24 PM)


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: revbobuk]
      #598423 - 01/04/08 07:32 PM
Quote revbobuk:

Hugh seemed to be suggesting that mics and stands are earthed for safety reasons) that would be a first for me - did you really mean that mic. stands should/must be earthed? I don't think I've ever seen that. Mics, yes. But stands? How would you do that?




I didn't mean to suggest that stands should or must be earthed. The metal body of mics are through the cable screen, obviosuly. Stands can become earthed because of contact with other earthed metalwork.

Performers usually get shocked becasue they are holding the guitars strings in one hand (which might be floating at half mains voltage or worse of the amp is missing it's protective earth), and then touch the mic (the body of which is earthed through the mic cable and mixer).

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Stewart Newlands



Joined: 27/03/08
Posts: 11
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #603389 - 13/04/08 12:38 PM
The venue must test socket outlets as a licence requirement in most cases. This is done formaly be electrical contractors or competent in house electrictians.

If sockets are not safe don't use them, walk away and if anyone hassels you remind them that electrical systems have to be safe as a requirement of the Electricity at work regulations 1989 under the HASAW act.

The IEE wiring regulations BS7671:2008 which now include temorary stuff for shows refer you to BS7909, which is being updated and is available in the 1998 form or as a draft 2008 version.

Both BS7671:2008 and the draft of BS7909:2008 recomend that the socket outlets are tested before use, for saftey particularly to check that the protective earth is continuious and that the resistence to ground is low enough to be effective in enableing the effective operating of protective devices.

I would as a minimum invest in a decent socket check plug with an indication of earth fault loop impedence.

More information about these things can be found at these links:

www.hse.gov.uk/electricity/socket1.htm
www.hse.gov.uk/pubns/indg247.pdf

http://www.martindale-electric.co.uk/sockets.htm#ez150

I am going to try to get permission to use section 5 of the proposed BS7909:2008 available as part of a free or low cost information sheet for lay electrical users.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Roidster



Joined: 14/04/08
Posts: 5
Re: Well, yeah, again, electric shocks from mics !! new [Re: Stewart Newlands]
      #603975 - 14/04/08 11:11 PM
well from my personal exprience,as a singer/guitar player
i found when getting a shock from a mic,usually come from a bad ground,due to plugs being in different wall sockets
and man it can hurt sometimes,my easy fix is,put my guitar
mixer and power amp all on the same wall socket,problem fixed
but this is really isn't a long term fix

there is bigger problem with the electrical in the house or building,some people call it dirty power,and could result
in a fire cause by an electrical problem,meaning the place could burn to the ground and you lose everything
and it might be good to have an electrical inspector
come in and check everything out

--------------------
Just a Musician


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
wigli
member


Joined: 31/01/04
Posts: 67
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #603980 - 14/04/08 11:36 PM
Did the venue have three phase power and if so was ALL the audio equipment plugged into the correct (ie. same ) phase?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Roidster]
      #604009 - 15/04/08 04:54 AM
Quote Roidster:

well from my personal exprience,as a singer/guitar player
i found when getting a shock from a mic,usually come from a bad ground,due to plugs being in different wall sockets
and man it can hurt sometimes,my easy fix is,put my guitar
mixer and power amp all on the same wall socket,problem fixed
but this is really isn't a long term fix




It is important to note, that if that socket has a faulty ground, this will not fix the real problem. Good grunds are important.

Quote:


there is bigger problem with the electrical in the house or building,some people call it dirty power,and could result
in a fire cause by an electrical problem,meaning the place could burn to the ground and you lose everything
and it might be good to have an electrical inspector
come in and check everything out




What most people call "Dirty power" is actually a bit different. It ranges in definition, but in general it tends to fall into the category of under or over-voltage power coming from a bad source, or overly taxed distribution. I have also seen it refer to poorly isolated power, leading to similar problems as above, for instance an elevator motor starting up causing the sound system to get an under-voltage as it draws power.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Mattmvb



Joined: 29/03/08
Posts: 49
Loc: Birmingham, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: Stewart Newlands]
      #604465 - 16/04/08 04:20 AM
Many thanks for the info and links. This is something that's been on my mind recently, ever since I got a nasty shock from a standard lamp of all things - although I am very gratefull that it wasn't anything more than nasty, and that it was me not one of my customers. It was a lamp we move round quite often, and poor design meant that every time it got moved it rubbed a little more insulation off the live cable... (I know that's meandering a bit off topic but bear with me)

I run a small independent venue and regularly have the electrics checked out. However this incident has brought it home to me that something could go wrong 5 seconds after the electrician walks out of the door, and he may not be back for 6 months to check it out again.

This line was an eye opener for me:

Stewart Newlands Quote:

If your socket tester cannot display the Earth Fault Loop Impedance, it should not be used to check whether a socket is adequately earthed and safe to use.




I guess I'll have to upgrade to a more expensive tester - the cost is easily justified as you can't put a price on peoples lives.

Sadly, in my experience, this line isn't right:

Quote Stewart Newlands:

The venue must test socket outlets as a licence requirement in most cases. This is done formaly be electrical contractors or competent in house electrictians.




Unfortunatley I've never seen or heard of this being an actual licence requirement. For example, my own licence has several conditions pertaining to safety such as all fire routes must be kept clear and spills must be mopped up imediately, but naff all about electrics. There is a legal obligation that eveything must be safe, but too many operators look at their licence as being the be all and end all of their obligations. Also, since the changeover to the new licencing laws, I've had 2 "taskforce" visits, which basically means that police, licensing, environmental health and fire officers all turn up together to make sure you're within the letter of the law, but they've never even looked at the electrics! And I know that's the case in various friends venues as well.

Quote Stewart Newlands:

If sockets are not safe don't use them, walk away and if anyone hassels you remind them that electrical systems have to be safe as a requirement of the Electricity at work regulations 1989 under the HASAW act.




To be honest I'd recommend going one further than that and notifying the EHO (Environmental Health Officer) of the situation. There are a small minority of operators who don't give a damn, but if something goes wrong we all get tarred with the same brush.

Remember, YOU may have the chutzpah to walk away and cancel your gig, but there will be a lot of up'n'coming bands who will happily take that risk for a bit of exposure. That said, please speak to the management first, it could be a new problem and most of us are decent folk who really don't want to see a performer get electrocuted on stage!

Rant over!

--------------------
One is too many, two is about right, but three can never, ever, be enough


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Stewart Newlands



Joined: 27/03/08
Posts: 11
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #604971 - 16/04/08 11:27 PM
You can find more information about Electrical Saftey at www.7909.org.uk which will be listing all sorts of stuff regarding BS7909:2008 and BS7671:2008 and entertainment.

There may be some NVQs in this area at some point starting with a level 2, but it is some way off just now.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Roidster



Joined: 14/04/08
Posts: 5
Re: Well, yeah, again, electric shocks from mics !! new [Re: Mattmvb]
      #604998 - 17/04/08 05:28 AM
Quote Mattmvb:

Many thanks for the info and links. This is something that's been on my mind recently, ever since I got a nasty shock from a standard lamp of all things - although I am very gratefull that it wasn't anything more than nasty, and that it was me not one of my customers. It was a lamp we move round quite often, and poor design meant that every time it got moved it rubbed a little more insulation off the live cable... (I know that's meandering a bit off topic but bear with me)




this guy i knew,was living in a house,but it wasn't the lamp he was getting shocks from
everytime he used any light switch in the house,he would get a nasty shock
it had gotten to a point were he would use a stick to turn on and off the lights,in his house
finally they had gotten an electrical inspector in
he shut the hydro off at the pole and told them
every electical wire that ran through out the walls
floor and ceiling had to be replaced,before they would hook
the power back up
he said to them they were lucky there was never a electrical fire
this was an older house with original wiring,so over time the wires had deteriorated

--------------------
Just a Musician


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
jbk



Joined: 28/10/07
Posts: 17
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #612902 - 07/05/08 09:21 AM
If your under pressure to get your sound-check done you can try sticking a D.I. box between your guitar and the amp and plug the XLR cable from the D.I. into a stage box. This should solve the problem on the night and the show can go on.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: jbk]
      #613231 - 07/05/08 09:30 PM
Quote jbk:

If your under pressure to get your sound-check done you can try sticking a D.I. box between your guitar and the amp and plug the XLR cable from the D.I. into a stage box.




Um. Not convinced about that. The pass through output that goes from the DI to the amp doesn't usually offer any isolation so it won't electrically separate the guitar and (potentially dodgy) amp. Also, most guitar amps are mic'ed which doesn't present any electrical problems so I can't see why you'd want a DI feed instead...
Personally, if there's dangerous electrics on stage, the gig can wait until it's sorted. The show doesn't have to go on if it means putting lives at risk.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
jbk



Joined: 28/10/07
Posts: 17
Re: Well, yeah, again, electric shocks from mics !! new [Re: Sheriton]
      #613293 - 08/05/08 06:51 AM
This is if your getting shocks from the mic because the guitar is not properly grounded. you ground it with the XLR into the stage box. It's not a channel your going to use , so it's got nothing to do with the guitar being miced. It works, and always has done. It's not a permanent and far from ideal solution but as I pointed out the show must go on!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: jbk]
      #613295 - 08/05/08 07:05 AM
Quote jbk:

...as I pointed out the show must go on!




It takes me about 5 minutes to wire a new edison onto a plug over here. The show must go on, but not at a dangerous cost.

I will admit to being a bit sleep deprived, but at first glance your solution may work, by providing a path to ground with a lower potential, but it is addressing the symptom instead of the problem. Add this onto the fact that removing the shield in an audio cable is not an uncommon occurance to prevent ground loops in a safer way, and you are left with no path to ground except through the performer.

Fix the problem, not the symptom. Especially when it takes a couple of minutes at most, and ensures someone's safety.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
ef37a



Joined: 29/05/06
Posts: 5624
Loc: northampton uk
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #640827 - 26/07/08 05:12 AM
Wigi brought the matter up but can I reinforce his statement regarding phases please?

It might be very tempting if you run out of outlets to just run another extension to another room. There is NO guarantee that the room is on the same phase and thus the voltage stress on the equipment is greatly increased. Futhermore the earth path resistance will almost certainly be increased.

In older building that have been "knocked about" it is even possible that a socket at one end of the room has been "pinched" thru' a wall from another phase. AFAIK there is no easy, safe, cheap way to test for this so as Hugh says, run eveything from one outlet or those as close together as possible. You can pull nearly six kW from a 13A double, enough for any SOUND system surely!

Dave.

--------------------
#They did not listen, they are not listening still...Perhaps they never will?#


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: ef37a]
      #640860 - 26/07/08 10:29 AM
Quote ef37a:

You can pull nearly six kW from a 13A double, enough for any SOUND system surely!





No you can't! You're likely to start a fire if you try. With most twin outlets, the most you can draw is around 20A; they're not designed to be able to supply 13A from both outlets simultaneously. There are some designs out there that can do so safely but these are the exception rather than the rule.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
ef37a



Joined: 29/05/06
Posts: 5624
Loc: northampton uk
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #640886 - 26/07/08 11:41 AM
Thank you Sheriton. I was basing my figures on a ring I have just put in using 32A trips.

Are you saying the OUTLETS will burn, because the cable can surely stand 32A?

Dave.

--------------------
#They did not listen, they are not listening still...Perhaps they never will?#


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #640896 - 26/07/08 12:31 PM
The sockets themselves can overheat as they're not designed to be able to supply that much current. I believe it's the point where the cables are connected at the back that is the weakest link.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
ef37a



Joined: 29/05/06
Posts: 5624
Loc: northampton uk
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #640908 - 26/07/08 12:58 PM
Well, I was not suggesting a pair of 3kW heaters!

Shall we meet at a 5kW but not a continous load? 20A is not 5k I admit at 230V but we always get 240+ here and that is pretty close.

Our new premises run 250 most of the time and has hit 254 now and again!

Dave.

--------------------
#They did not listen, they are not listening still...Perhaps they never will?#


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: ef37a]
      #640918 - 26/07/08 01:18 PM
On the phase thing, I would note that running systems across multiple phases is actually NOT a problem (And is done routinely on largish gigs (32A TP+N is a much smaller and lighter cable then 63A SP)), there is 400 odd volts phase to phase sure, but as a minimum of 4 faults are required to end up with two bits of exposed metalwork being live to different phases (Two earth faults and two phase->case faults) this should be a completely negligible risk if your electrical maintenance regime is even halfways competent.

The large earth loop that can result from plugging into multiple locations can cause circulating currents in the screen connections, but as long as nothing has a pin one problem, and everything is balanced, that rarely causes hum (And if it does, just fix the gear already).

One thing to watch with ring mains is that you never know what else is connected to them (Think Ice makers!), but for a general bar gig I would probably be quite happy to run a PA off one, sound requires remarkably little RMS current (and it is that, not smallish short term peaks that causes problems). Lighting is of course another matter.

I would second the advice to get a good socket tester, and getting the local theatre sparks to PAT your gear for you occasionally is never a bad thing (Normally costs a few pints). Hell just opening up the plugs and tightening all the screws once a year goes a long way.

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
ef37a



Joined: 29/05/06
Posts: 5624
Loc: northampton uk
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #640921 - 26/07/08 01:31 PM
Ok Dan,

I take you point about phases. I based my warning on an experience at a factory where I was a general handyman. The power on one wall in the refrectory failed one hot afternoon and there were 3 snack chillers in there. I quickly ran in a couple of mains leads from the testroom outlets about 15mtr away the other side of a breezeblock wall.

I was roundly castigated the next day by the visiting sparks re phase dangers. I did think at the time that you would have to be bloody unlucky.....

Dave.

--------------------
#They did not listen, they are not listening still...Perhaps they never will?#


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: ef37a]
      #640934 - 26/07/08 03:06 PM
A long time ago there was a requirement in the 'wiring regulations' (BS 7671) to separate all sockets on different phases by 2M, but that was removed many years ago.

There are however still many site electricians that seem to be wedded to following this practise to the point of insisting on it.

I just had some 200 channels of lighting dimmer installed at work we did try to keep it to one phase per bar (not always successfully) on the grounds that it doesn't hurt and there is an outside chance that it may help some day, but it is not something to get overly worried about.

I do however try to keep all the backline on one phase as in my experience this tends to be where the really dodgy stuff turns up (And the venue often does not have easily applied control over it).

FWIW My amp racks (and fixed signal processing) are fed from a three phase supply locally broken down to give the required single phase feeds, are installed right next to the main dimmer racks (the location was convenient), and the whole thing is totally silent.

An awful lot of the time you get moans from sound types about buzz from dimmers it is more a reflection on the sound companies engineering then it is venue or lighting companies...

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
IvanSC



Joined: 08/03/05
Posts: 7760
Loc: UK France & USA depending on t...
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #654327 - 08/09/08 07:10 AM
Just to breathe life into this sticky again, we nearly lost 3 more to electric shock at the weekend.

Kim Rew, Lee Cave Berry & Ted Koehurst were playing a gig with a dodgy 3 phase installation & lost all 3 amplifiers, plus Ted got well and truly zapped.
No dead bodies, but how close do you need to get?
The worrying thing is that the amps worked for one set before frying (and predictably in at least one case shorting to the input jack, which was earthed to the chassis)
Ths was not a bad earth, this was incorrect voltage (440)which makes it even scarier.
I don`t have all the details yet but will try to post once I get in touch with one of them.

RDF`s don`t always get everything folks - especially if you are playing outdoor events/festivals, it pays to carry a good mains tester as well as your own individual RDF device.
Cheap life insurance.

--------------------
Me? But I`m such a loveable old bugger!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
thatsrightmynameisjo...



Joined: 05/10/08
Posts: 6
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #664077 - 05/10/08 01:10 PM
Hi, I've just been reading through this thread and despite not understnading anything, it worries me.

I've had a few gigs where I have been getting painful shocks off the mic when I touch it to sing (I play guitar and sing).

I don't know anything about electronics so would anyone be able to explain to me (in simpler terms) what I would have to do/buy to ensure that both me and my bandmates are safe both at gigs and at practice?

Thanks very much
Adam


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: thatsrightmynameisjohn]
      #664090 - 05/10/08 02:09 PM
The first thing I'd suggest is to get someone electrically competent to have a look at your guitar amp. The main cause of experiencing a potential difference between your mouth and the mic is that the earth in the guitar amp isn't doing its job which causes the guitar strings to float up to 110v. You won't notice this until you touch something earthed like a microphone.
1st thing to check is inside the mains plug - make sure the earth wire is well & truly connected to the earth pin.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Paul Soundscape



Joined: 27/06/06
Posts: 722
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #664098 - 05/10/08 02:43 PM
a socket tester is also a useful tool,
check every socket you plug your gear into to make sure its wired properly and is earthed

--------------------
Live Sound and Studio Engineer


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Statick



Joined: 01/09/04
Posts: 1024
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #664127 - 05/10/08 05:41 PM
on the second night of our most recent tour, the singer/guitarist got a nasty zap off her mic during soundcheck.

turned out it was the 4-way at fault (the earth lead had come loose from the plug), but anyway the next day i went and bought a simple £10 mains tester. we used it before every show for the remainder of the tour, and found several instances of missing earth and live/neutral reversed, but in all cases it was extension leads that were at fault - the wall sockets themselves were all fine.

so the moral is, i guess, test all the extensions as well, especially if it's venue-owned gear and not your own.

--------------------
Statick Audio


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
thatsrightmynameisjo...



Joined: 05/10/08
Posts: 6
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #664183 - 05/10/08 08:12 PM
Thanks for the advice, I've got a couple of mates who are sparkies so I'll get one of them over to check my gear out.
Can someone link me to a good socket tester that will test for everything and is easy to use?

I tried google but I don't really know what to look for..

Cheers


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: thatsrightmynameisjohn]
      #664200 - 05/10/08 09:09 PM
This one should be a good starting point.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
thatsrightmynameisjo...



Joined: 05/10/08
Posts: 6
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #664214 - 05/10/08 09:45 PM
Cheers mate


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Mattmvb



Joined: 29/03/08
Posts: 49
Loc: Birmingham, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #664235 - 05/10/08 10:37 PM
Thanks to this thread I've altered my weekly routine. Previously I'd always test my emergency lights and fire alarm on a tuesday morning; I've now added socket testing to this list.

I've come up with a theory that may or may not be right, but if it is completely wrong it can't do me any harm anyway. Basically, I reckon that terminal screws in plugs and sockets in locations that are subjected to high sound levels must be more likely to work loose over time because of the vibrations - you can also add in the vibrations from the footfall of a couple of hundred excited people - and of course the body fall of a couple of excited drunk people...

Please keep the safety advice coming.

Cheers,

Matt

--------------------
One is too many, two is about right, but three can never, ever, be enough


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: Mattmvb]
      #665127 - 08/10/08 04:48 AM
Mattmvb,

more relevant is the usage: being regularly plugged/unplugged, thrown into boxes/flightcases amd transported in vehicles with all the resultant periods of vibration. This handling will affect virtually any screw termination after a period of time -something that normal office mains extensions will not have to endure.

I seal mains screw terminals with a blob of nail-varnish to combat this (my original background is in electrical engineering and instrumentation and calibration adjustment trims are always sealed in this manner after any change); this seems to prevent loosening.

I also check the earth integrity of my cable very regularly (the most important electrical connection) and I visually check all my mains cables every time they are unpacked for a gig and repacked at the end of the night Cables are a rig's weakest link and safety and reputation are of paramount importance to any PA company.

get a mains tester and check your extension leads as you plug-in during set-up. buy a beer for an electrician mate and get him to check all your cables once a year...

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Mattmvb



Joined: 29/03/08
Posts: 49
Loc: Birmingham, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: Nathan]
      #665783 - 10/10/08 12:24 AM
Quote Nathan:

Mattmvb,

I seal mains screw terminals with a blob of nail-varnish to combat this (my original background is in electrical engineering and instrumentation and calibration adjustment trims are always sealed in this manner after any change); this seems to prevent loosening.






Thanks for the tip Nathan.

I've also learnt another lesson the hard way. To cut a long story short I'm off to B&Q in the morning to buy some shatterproof plugs and 4-way adaptors. Fortunately nobody came to any harm but it was quite worrying to see a guitarist lose his balance whilst setting up, tread on a plug and watch half of it break off!

With regard to the cable testing, I'm fortunate to be located next door to a large theatre so no worries there - although my mains voltage can be a bit variable when they've got a big show on!

Thanks,

Matt

--------------------
One is too many, two is about right, but three can never, ever, be enough


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: Mattmvb]
      #665819 - 10/10/08 08:29 AM
Quote Mattmvb:

To cut a long story short I'm off to B&Q in the morning to buy some shatterproof plugs and 4-way adaptors.




Rubber plugs & sockets are your friend. They cost more, but can take far more abuse.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: Sheriton]
      #666335 - 12/10/08 10:04 AM
Duraplug and Permaplug are the brands to look for, you can get them both in the larger B&Qs, but it might do you to buy from Canford as boxes of ten, etc will work out cheaper.

if you can't find the above brands, look for plugs with BS1363/A on them as the A means they comply to the more physically robust spec.

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Steven Montgomery



Joined: 06/06/06
Posts: 39
Loc: Northern Ireland
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #674267 - 02/11/08 09:53 PM
You just gotta make sure that the pa and the amp are running of the same circuit. If your not sure about the wiring of the room buy yourself a proper RCD and plug it into the wall, and run everything from there. For most small things you should be grand, for bigger stuff make sure you jump up to 16a or something of the sorts as soon as you come out of the wall, and a wee distro wouldnt go a miss.

--------------------
Monty


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Eon



Joined: 11/05/09
Posts: 2
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #733859 - 11/05/09 04:41 PM
I've just started as an house engineer at a rather small club and just last weekend the guitarist started getting shocks, didn't think it was this big of a deal and will check all the sockets right away.

But, I've got a question, there is a smoke machine hooked on the same fuse as the backline and mixer, could this be a factor in shocks? It's all metal and stands to the side of the stage.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Eon]
      #733866 - 11/05/09 04:54 PM
Quote Eon:


But, I've got a question, there is a smoke machine hooked on the same fuse as the backline and mixer, could this be a factor in shocks? It's all metal and stands to the side of the stage.




Only if the guitarist is touching it as well.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: seablade]
      #733870 - 11/05/09 05:12 PM
Actually if the guitar amp and fogger are plugged into the same outlet, and that outlet is not grounded, then yes this could also be a problem.

But the end result is that it is important for ALL equipment that shipped with a ground connection, be in fact grounded.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #733893 - 11/05/09 07:06 PM
The last guitar amp that came to one of my venues: I could see it would fail its PAT before I even got anywhere near it! The guitarist was busy stuffing the mains cable further in to the plug as the outer insulation had been stripped back far too far and the strain relief was obviously ineffectual. I opened the plug and found a 13A fuse instead of the 5A that should have been in there for the size of mains cable. And the earth wire had been cut. Not worked its way loose but cleanly cut.

I rewired it, did the rest of the PAT and handed it back to him with an explanation of why it wouldn't kill him now.

Lessons learnt: be VERY suspicious of guitar amps when it comes to electrical safety.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Ian Savage



Joined: 16/12/07
Posts: 611
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #733954 - 11/05/09 10:46 PM
Thanks for all this; I'm usually wireless live but our singer's been getting some nasty buzzes of late both live and in the rehearsal room. Musy pick up some RCDs and a socket tester as a matter of urgency.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: Ian Savage]
      #751239 - 09/07/09 07:43 AM
This theme about singers and guitarists getting twitches from mics seems to be a recurring endemic, so I thought I'd offer some advice.

If you're getting shocks off a mic then don't just stuff a pop-shield over it, find out what's happening; either the mic is live or you're greounding yourself on the mic because something else is.

check that the earth wire is intact and connected in the plug to your PA amps and mixer, your guitar amps and any mains leads and extension blocks that supply it.

Don't take any excuses whatsoever from any guitarist who's removed an earth. None. reconnect of f*** off. Funerals are not as fun as gigs, even for Emo bands.

The only time that a plug with no earth is ok is if the appliance is "double insulated" (class2) and carries the square-inside-a-square symbol. No symbol and no earth? get someone to look at it before you use it!

Never use any mains extension that doesn't have an earth unless it is terminated in a two pin socket (like a lawnmower extension lead, see above for class2) if it has a 13A three-pin socket, appliances that require an earth could be plugged in and would not have their necessary earth (you'd be prosecuted if there was an accident).

If you are getting shocks and you're not sure what's at fault, buy or borrow a multimeter and put it on the mains (AC) setting -usu 250, 500, 1000V switch; measure between the mic grille and a water pipe or sink top or earth pin on a 13A socket, anything more than a couple of volts (high impedance floaty mains-hum pickup) is a problem and needs investigating. Try it from the bridge or strings of the guitar and see if there's any voltage. Generally anything above 50Vac will cause you a tingle when you put your lips on an earthed mic grille. the most common reading if there is a compromised earth is half normal mains voltage -about 120V. Sort it look at the earth in any mains, IEC and extension leads.

It's always a good idea to have your own 30mA RCD plug. Then you know if you touch 240V it will trip and protect you. Press the test button regularly to make sure it trips when mains is on. Those mains plug testers with three lights to show whether your earth is there and Live and Neutral are right-way-round are good too -I check all venue supplies like this.

check your mains and extension leads every time they come out of or go back into your bag/box. if there is any damage, wires showing, scuffs, cracks in plugs, etc -sort it. PAT testers do that as the first part of the test and won't even plug it into their tester if if fails the visual test (you'll get charged your test fee as a fail, and a retest fee after they've fixed it). Open up you plugs and make sure the wires are correctly terminated, looks tidy, shows no sign of overheating, fraying, fuse is correct and the screws are all tight.

If your gear looks tidy and looked over, most venues will not hassle you for PAT test certs etc. They will raise eyebrows/refuse use of gear if it looks shot. PAT test once a year is good practice for safety and hassle-free gigging, but must be supplemented by visual checks. Look on the HSE website for charts of what to be looking for (HSE think the PAT sticker movement has gone just a little to far and are quite keen for people to be educated about appliance safety as an alternative to compulsory testing in many cases)

Remember ggiging can be hard on your electrical gear, safety is paramount and your gear reliability is your gig reputation -look out for issues before they ruin your show or hurt someone.

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
eggle5



Joined: 15/10/07
Posts: 52
Re: Well, yeah, again, electric shocks from mics !! new [Re: Nathan]
      #757821 - 27/07/09 11:34 PM
Quote Nathan:

This theme about singers and guitarists getting twitches from mics seems to be a recurring endemic, so I thought I'd offer some advice.

If you're getting shocks off a mic then don't just stuff a pop-shield over it, find out what's happening; either the mic is live or you're greounding yourself on the mic because something else is.

check that the earth wire is intact and connected in the plug to your PA amps and mixer, your guitar amps and any mains leads and extension blocks that supply it.

Don't take any excuses whatsoever from any guitarist who's removed an earth. None. reconnect of f*** off. Funerals are not as fun as gigs, even for Emo bands.

The only time that a plug with no earth is ok is if the appliance is "double insulated" (class2) and carries the square-inside-a-square symbol. No symbol and no earth? get someone to look at it before you use it!

Never use any mains extension that doesn't have an earth unless it is terminated in a two pin socket (like a lawnmower extension lead, see above for class2) if it has a 13A three-pin socket, appliances that require an earth could be plugged in and would not have their necessary earth (you'd be prosecuted if there was an accident).

If you are getting shocks and you're not sure what's at fault, buy or borrow a multimeter and put it on the mains (AC) setting -usu 250, 500, 1000V switch; measure between the mic grille and a water pipe or sink top or earth pin on a 13A socket, anything more than a couple of volts (high impedance floaty mains-hum pickup) is a problem and needs investigating. Try it from the bridge or strings of the guitar and see if there's any voltage. Generally anything above 50Vac will cause you a tingle when you put your lips on an earthed mic grille. the most common reading if there is a compromised earth is half normal mains voltage -about 120V. Sort it look at the earth in any mains, IEC and extension leads.

It's always a good idea to have your own 30mA RCD plug. Then you know if you touch 240V it will trip and protect you. Press the test button regularly to make sure it trips when mains is on. Those mains plug testers with three lights to show whether your earth is there and Live and Neutral are right-way-round are good too -I check all venue supplies like this.

check your mains and extension leads every time they come out of or go back into your bag/box. if there is any damage, wires showing, scuffs, cracks in plugs, etc -sort it. PAT testers do that as the first part of the test and won't even plug it into their tester if if fails the visual test (you'll get charged your test fee as a fail, and a retest fee after they've fixed it). Open up you plugs and make sure the wires are correctly terminated, looks tidy, shows no sign of overheating, fraying, fuse is correct and the screws are all tight.

If your gear looks tidy and looked over, most venues will not hassle you for PAT test certs etc. They will raise eyebrows/refuse use of gear if it looks shot. PAT test once a year is good practice for safety and hassle-free gigging, but must be supplemented by visual checks. Look on the HSE website for charts of what to be looking for (HSE think the PAT sticker movement has gone just a little to far and are quite keen for people to be educated about appliance safety as an alternative to compulsory testing in many cases)

Remember ggiging can be hard on your electrical gear, safety is paramount and your gear reliability is your gig reputation -look out for issues before they ruin your show or hurt someone.



Ur comments are well founded & appreciated and have been copied onto our local music web scenes cos it's an on going problem that never seems to go away!!!!
The number of amps/mixers I've come across on stage with the earth removed beggars belief. I've stopped bands playing because of this and refused to do the sound for them. At the end of the day a 5 amp fuse versus an electrocution - no contest but there are guys out there still doing this - I will not work with them and tell them at the sound check. Get an RCD from B & Q - it ain't rocket science & it's a cheaper way to save your life!!!!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Stewart Newlands



Joined: 27/03/08
Posts: 11
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #759061 - 01/08/09 05:51 PM
There is lots to read on the 7909 website

A website dedicated to Electrical safety for Entertainment and related purposes

In particular: Bs7909:2008 The Code of practice for temporary electrical systems for entertainment and related purposes

Loads of links and advice on how to use electricity well.

http://www.7909.org.uk

Don't forget if you think a venue is unsafe apply to the local council for a licensing review asking for a section 182 condition on electrical safety to be added!

Edited by Stewart Newlands (01/08/09 05:54 PM)


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
IvanSC



Joined: 08/03/05
Posts: 7760
Loc: UK France & USA depending on t...
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #759147 - 02/08/09 07:33 AM
Was talking to My Mate Ted last night at a party & he told me the story of a recent near disaster he experienced.

They use a tester etc and normally have no probs with mains.
They were playing an outdoor gig and some clown had mis-wired the three phase supply so that two phases were hooked up to phase and neutral, givinbg a potential of 460 volts across the supply.

Ted said his amp had never sounded so good for the first set, then all of a sudden everything was smoking and he was flopping around like a beached herring, still holding the offending (lethal) guitar lead. Fortunately the bass player put his foot on ted`s hand holding the lead and got him off it, but the backline was fried and poor old Ted was in a bad way for some time after.

And of course he and a mate have now gone into business making this cool little box that measures the potential between ALL connections (not just phase and earth and neutral & earth)and shuts the supply down if anything exceeds 260 volts.
So far three PA hire companies have bought and I suspect he will get a lot of other customers.
Around £100, which is way cheaper than the next available thing at about £400

--------------------
Me? But I`m such a loveable old bugger!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
turbodave



Joined: 25/04/08
Posts: 2105
Loc: derbyshire uk
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #759158 - 02/08/09 09:07 AM
Hi Ivan, so do I google "My mate Ted.co .uk" or will you spill the beans?Dave

--------------------
My head hurts!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
adamb1026



Joined: 05/10/09
Posts: 60
Loc: Belfast, N.Ireland
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #776231 - 05/10/09 09:54 PM
This has happened on a number of occasions with our band most recently on Saturday night. Our lead vocalist was receiving shocks on his microphone. The vocal is the only thing that goes into the mixer since it was such a small venue and we don't own any bass bins yet.

The mixing desk and power amp was plugged into a Surge Protected 4 way adapter into what looked like a slightly dodgy plug, but we have played there on many occasions and this was the first time this happened.

We then just plugged in the mixer into the plug and it worked fine.

Our gear has been lugged in and out of vans and cars for nearly 7 years now, with updates and changes of course, so I can see an aspect of that affecting things, but the mixing desk is usually kept in good nick.

Just a few quick questions, because this has been plaguing us for a while, and myself.

1. Are surge protected 4 way plugs recommended? I have heard rumors they are not good for powering amps etc. So just to confirm before i go out and buy some

2. Is using many separate wall sockets the best method to combat electrical shocks?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Mike Stranks
active member


Joined: 03/01/03
Posts: 3058
Loc: Oxford, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: adamb1026]
      #776313 - 06/10/09 08:44 AM
Quote adamb1026:

This has happened on a number of occasions with our band most recently on Saturday night. Our lead vocalist was receiving shocks on his microphone. The vocal is the only thing that goes into the mixer since it was such a small venue and we don't own any bass bins yet.

The mixing desk and power amp was plugged into a Surge Protected 4 way adapter into what looked like a slightly dodgy plug, but we have played there on many occasions and this was the first time this happened.

We then just plugged in the mixer into the plug and it worked fine.

Our gear has been lugged in and out of vans and cars for nearly 7 years now, with updates and changes of course, so I can see an aspect of that affecting things, but the mixing desk is usually kept in good nick.

Just a few quick questions, because this has been plaguing us for a while, and myself.

1. Are surge protected 4 way plugs recommended? I have heard rumors they are not good for powering amps etc. So just to confirm before i go out and buy some

2. Is using many separate wall sockets the best method to combat electrical shocks?




Surge protection will not protect against dodgy earths - which is almost certainly what was happening here.

I suggest you get yourself a socket tester - you can get them from Maplins - which will let you see if the wiring in the socket is as it should be. Any problems, then don't use that socket and tell the venue management that they have a serious problem which needs fixing pronto.

But that's not enough. Always connect to sockets using an RCD current dumper - widely available from DIY multistores. And if you have several mains extensions daisy-chaining then put an RCD on each link. RCDs only cost a few pounds and could save someone's life.

There's no advantage in connecting to multiple wall sockets as long as you're not overloading one socket. In fact, using multiple sockets raises the possibilities of introducing ground/earth loops.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: adamb1026]
      #776333 - 06/10/09 09:35 AM
Quote adamb1026:

This has happened on a number of occasions with our band most recently on Saturday night. Our lead vocalist was receiving shocks on his microphone. The vocal is the only thing that goes into the mixer since it was such a small venue and we don't own any bass bins yet.





Does your lead vocalist play guitar?

The body of the microphone will be connected to the ground / earth of the mixing desk. If the mic body was at a potential that would cause shocks, it's likely that the case of the mixer would be at this same potential. Did anybody notice any tingles when touching the mixer?

In order to get a shock, you have to be touching two things at different potentials at the same time. The mic is one of those things; to be fair to it, the mic is usually not the culprit as it is usually at ground potential.

99% of the time, the problem is with a singing guitarist's amp. Despite the title of this thread, the mic is very rarely the cause.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
adamb1026



Joined: 05/10/09
Posts: 60
Loc: Belfast, N.Ireland
Re: Well, yeah, again, electric shocks from mics !! new [Re: Sheriton]
      #776356 - 06/10/09 10:55 AM
Quote Sheriton:

Quote adamb1026:

This has happened on a number of occasions with our band most recently on Saturday night. Our lead vocalist was receiving shocks on his microphone. The vocal is the only thing that goes into the mixer since it was such a small venue and we don't own any bass bins yet.





Does your lead vocalist play guitar?

The body of the microphone will be connected to the ground / earth of the mixing desk. If the mic body was at a potential that would cause shocks, it's likely that the case of the mixer would be at this same potential. Did anybody notice any tingles when touching the mixer?

In order to get a shock, you have to be touching two things at different potentials at the same time. The mic is one of those things; to be fair to it, the mic is usually not the culprit as it is usually at ground potential.

99% of the time, the problem is with a singing guitarist's amp. Despite the title of this thread, the mic is very rarely the cause.




Thanks Mike, will use your advice

Also, do you have any links to where I could buy a RCD damper? I've just been looking on maplins and cant seem to find one.

Thanks again


Sorry, should have been more specific, he was receiving shocks to his lips rather than the casing. I don't think he received any shocks from the desk.

And yes he does play guitar . Out of my ignorance, how does his amp become the problem?

Some of the venues we play really don't accommodate bands well. They just find an empty space and tell us to setup there. Since the smoking ban has come into our country, in one venue, we basically play beside the door to where people have to get outside. We used to take the whole area, but now since we are squeezed to one side, my bass head has almost become a weapon lol

Edited by adamb1026 (06/10/09 10:56 AM)


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: adamb1026]
      #776360 - 06/10/09 11:14 AM
Quote adamb1026:


Also, do you have any links to where I could buy a RCD damper? I've just been looking on maplins and cant seem to find one.





Not sure where the word damper came from but it's this kind of thing that you're after. I can't vouch for that particular model as I've never used one but any DIY store will sell you an RCD also.

Quote adamb1026:


And yes he does play guitar . Out of my ignorance, how does his amp become the problem?





A lot of misguided guitarists cut the mains protective earth in their amp, believing it to be the way to eradicate hum from their rig. Have a read right through this thread for more details. I know it's long, but it may just save someone's life. Seriously. Far too many guitarists have been killed through this stupidity. Get all of your kit PAT tested regularly if you don't already do so. That will show up any potentially dangerous faults like a lifted earth.
And if your guitarist has disconnected the earth, beat him around the head with the amp until he sees sense. There is never EVER any reason for doing so. Under any circumstances. EVER.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
adamb1026



Joined: 05/10/09
Posts: 60
Loc: Belfast, N.Ireland
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #776367 - 06/10/09 11:24 AM
I dont think he has cut the earth, but I'll check it out in any case and give him a good smack if he has.

Thanks very much for all of your help.

Must go for a walk down to Maplins

Edited by adamb1026 (06/10/09 11:25 AM)


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: adamb1026]
      #776418 - 06/10/09 12:59 PM
Quote adamb1026:

I dont think he has cut the earth, but I'll check it out in any case and give him a good smack if he has.




A bad socket can cause a similar effect. Pretty much if the ground is disconnected ANYWHERE in the power chain, this NEEDS to be fixed. No exceptions. This is why people are suggesting the socket tester, as it allows you to quickly and easily see if a socket is good, never assume it is.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Mike Stranks
active member


Joined: 03/01/03
Posts: 3058
Loc: Oxford, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #776424 - 06/10/09 01:17 PM
If he's getting shocks to his lips, there's a possibility that it was static electricity! (NB. That doesn't mean you can ignore all the other stuff we've written! )

I was once very agressively berated by a singing guitarist when he got a lip-shock. I knew all the gear was OK, but checked it anyway - no problems found, all earths good. Eventually I tracked it down to him wearing some synthetic materials and some synthetic-soled trainers. He was his own little Van der Graff Generator and then earthed himself through the mic capsule basket and its connections. That's not to take away from the static shock you get though; it happened to me once and it ain't funny!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #776568 - 06/10/09 09:13 PM
Quote:


1. Are surge protected 4 way plugs recommended? I have heard rumors they are not good for powering amps etc. So just to confirm before i go out and buy some




Not particularly, at best the protection is marginal, they often fail silently and they can contaminate the power ground (which really shouldn't matter, but often does, particularly with unbalanced gear).

They only do what any competent power supply designer should be doing anyway.
Quote:


2. Is using many separate wall sockets the best method to combat electrical shocks?




Nope, using a few sockets that you have tested and know to be correctly wired and earthed, and keeping all your gear in good repair is the best way to avoid shocks, and RCDs are (while not foolproof) a good way to increase your chances of surviving one.

A shock should be an indication that something (several things) has gone badly wrong, and should always be a signal to stop and fault find then fix whatever the problem is (And then review your maintenance, it should never have gotten that far).

Sorry, but IMHO a shock is almost always an indication that someone has screwed up, as it really should require at least 2 faults to cause one.

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
adamb1026



Joined: 05/10/09
Posts: 60
Loc: Belfast, N.Ireland
Re: Well, yeah, again, electric shocks from mics !! new [Re: Mike Stranks]
      #777113 - 08/10/09 12:19 PM
Quote Mike Charles:

If he's getting shocks to his lips, there's a possibility that it was static electricity! (NB. That doesn't mean you can ignore all the other stuff we've written! )




lol well it has happened on a few occasions, so through reading this topic, I can pretty much confirm it is the plugs , but I will keep that in mind next time it happens.

Thanks dmills on the advice especially about surge protectors.

We do have an large amount of gear. Particularly our lead guitarist has 8 pedals through a Behringer 12 set pedal board, which I thought was maybe could be a concern for future electric problems. Again excuse my ignorance if it isn't.

I think I'm going to persuade him and invest in a hard case for the mixer and power amp after telling him about this and to genuinely keep his mixer in good nick .


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: adamb1026]
      #777579 - 09/10/09 11:30 PM
if this mic-grille shock has happened multiple times in different venues, it suggests that the problem might be a fault of your band's gear somewhere (the common factor).

If you have a multimeter, set it to its 250V, 500V or 1000V AC setting and measure between the mic grille and a radiator or water pipe) If there's more that a couple of Volts then you could have a mains earth-issue in your PA or mixer supply.

If that's normal, but measuring between your guitarist's bridge or strings and the radiator/pipe gives you a reading, then the issue is with the guitar amp or mains plug/cable supplying it. What you're looking for is voltage on something that should be earthed.

Post or PM me if you need further help.
Nathan.

>

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
adamb1026



Joined: 05/10/09
Posts: 60
Loc: Belfast, N.Ireland
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #778709 - 13/10/09 06:52 PM
That's great Nathan thanks.

My dad should have a multimeter lying about in the garage somewhere who is a qualified electrician, so I can tell him about your technique and he can guide me a bit further as well.

Appreciate the help.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: adamb1026]
      #779694 - 17/10/09 10:36 AM
establish that there is an issue between bridge and mic grille first by measuring directly between them, if it reads about 120V approach with caution! This will rule out a static electricity issue, then measure to each from the water pipe. Bear in mind that this trick can also dig out problems with installed wiring earths, and also that not all central heating systems are earthed (although they should be bonded).

I usually find that its an earth problem in a mains cable leading to the guitar amp, but this method has traced problems to loose earths in extension leads supplying the PA mixer too.

>

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Nathan]
      #779720 - 17/10/09 11:32 AM
Yes, you need to be very logical and thorough when trying to track down a potential satefty earth problem like this.

There are lots of earth interconnections between the wall socket and the guitar, and every single one has to be good to be safe... so work through carefully and logically fromt he wall socket.

Start with a mains plug tester, as recommended above to check the wall socket(s) and do that at every single venue you use every single time you use it. I lost count years ago of how many tims I've found duff, unsafe sockets in public venues.

If the socket is safe and properly earth bonded, then work through all your mains extension boards and extension cables. The first check -- and one you should do everytime you pack and unpack you gear is a visual one, looking for cracks, cuts or crushes to the cable or any damage to the plugs of sockets -- any sign of physical damage requires careful investigation before use.

You can test the extension cables and boards with a multimeter but a quick and easy way is to use the mains socket tester again by plugging the extension cable of distribution board into the wall socket and then plugging the tester into each socket on the board or cable to check they are all okay. It is possible for individual sockets in extension boards to fail too...

If all the mains distribution stuff tests fine, then you'll need to move on to the IEC mains cables or the equipment itself if it uses captive mains leads. This is where you'll need to use a multimeter with a resistance or continuity mode. Don't plug the IEC leads into the mains -- instead put one probe onto the large mains plug earth pin and the other into the offset central earth receptacle on the IEC socket. You should get a reading of zero ohms or 100% continuity.

If it's a captive cable, then check between the mains plug earth pin and the metalwork on the equipment -- unless the label has the double-insulated symbol (a box within a box), in which case you won't get any continuity at all, by design.

Static shocks can be unsettling but are rarely any real problem and perversly do indicate that the system is probably properly earthed!

One way to determine whether you have a serious safety earth problem or just static shocks is to find out if the shock happens constantly or just briefly now and again.

A safety earth problem will mean that every single time someone bridges between something properly earthed (usually the mic) and the faulty part of the system (usually the guitar amp), they will get a shock (or, hopefully, trip the RCD!) and that the shock continues for as long as they are in contact (or until the RCD trips).

If it's a static shock, the first time they touch anything earthed they will discharge themselves and feel the brief moment of shock but thereafter they won't feel anything while they remain in contact. And if they touch it again a few moments later they won't feel a second shock either.

Only after they've shuffled around on the carpet or danced about to recharge their clothes will they build up their own static potential enough to feel a shock when discharging again through something earthed.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
the muppet



Joined: 27/08/04
Posts: 1010
Loc: with my head stuck up my a£se...
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #796104 - 14/12/09 03:27 PM
Hugh,

As this topic comes up time and time again, and as a lot of us return to the same venues, would it be with our rights or the rules of the forum to start "naming and shaming" the venues that have dodgy supplies and such like.

I've been touring now for quite some time and there are venues out there that I'm always very dubious about pluging even my phone charger into, but those where I have even refused to plug into the heavier mains supplies.

One, which shall for the mean time remain as Venue X had 2x 32a single ceeforms on each side of the stage, mounted on the floor. Both were live-neutral reversed and one was so badly damaged that I couldn't even plug my rack in (we have EMO distro in all our racks which has those handy neon indicators)

When speaking to the in-house electrician about why I wasn't about to plug my gear in, he said "Everybody uses them, it's ok for them, it can be ok for you!"

This isn't just a small pub somewhere, this is a major national venue. We shouldn't be taking this kind of attitude and I refuse to go back and have mentioned it to the relevant authorities, but I think as most of us know, this can't happen again.

PM me if you want to chat about how we do this

Cheers

Ben

--------------------
The early bird may catch the worm, but it's the second mouse that gets the cheese!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: the muppet]
      #796132 - 14/12/09 05:31 PM
I can certainly understand your frustration, Ben, but I think I'll need to take some advice before allowing a name and shame thread... tempting though it would be.

Leave it with me for a few days please.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
TheChorltonWheelie



Joined: 22/09/09
Posts: 867
Re: Well, yeah, again, electric shocks from mics !! new [Re: Mike Stranks]
      #796142 - 14/12/09 06:05 PM
Quote Mike Charles:

If he's getting shocks to his lips, there's a possibility that it was static electricity! (NB.




I'll tell you now, I am very susceptible to static - I even have to be careful when I get out the car, by earthing myself first, and I'm not kidding either. I regularly get shocks from mic's, and all my kit properly earthed/pat tested (which I did as a result of having read a thread like this years ago).

Some people are just unlucky.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
the muppet



Joined: 27/08/04
Posts: 1010
Loc: with my head stuck up my a£se...
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #796190 - 14/12/09 10:46 PM
Quote Hugh Robjohns:

I can certainly understand your frustration, Ben, but I think I'll need to take some advice before allowing a name and shame thread... tempting though it would be.

Leave it with me for a few days please.

Hugh




Of course!!

I will say that 99% of venues we go to are spot on and I wouldn't have a word said against them.

I understand it's very much a case of the venue could be the safest place to plug into but a bands gear is shot to bits, and vice versa.

It just seems to me that so many legislations are out there now to stop this sort of thing happening, it happens on such a regular basis.

This may be slightly off topic, but when, in a time when health and safety is killing our industry, is a lack of health and safety potentially risking our lives?

I'm sorry if I seem to have come across all stroppy about this, but judging by the number of posts here, it's obviously a major concern

Ben

--------------------
The early bird may catch the worm, but it's the second mouse that gets the cheese!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: the muppet]
      #796195 - 14/12/09 10:59 PM
Quote the muppet:

As this topic comes up time and time again, and as a lot of us return to the same venues, would it be with our rights or the rules of the forum to start "naming and shaming" the venues that have dodgy supplies and such like.




I've discussed it with Ian, and as you probably suspected, the word is no. It's just too risky if someone doesn't get their facts straight (accidentally or even deliberately), or the venue improves and the thread isn't updated. It would leave SOS open to being sued, and that really wouldn't be a good idea.

So, sorry. But no. I think the best course of action would simply be to bring any venue with poorly maintained electrical supplies to the attention of the appropriate regulatory bodies -- the local council or the HSE.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
feline1
active member


Joined: 23/06/03
Posts: 3651
Loc: Brighton, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #796271 - 15/12/09 11:37 AM
Quote Hugh Robjohns:

Quote the muppet:

As this topic comes up time and time again, and as a lot of us return to the same venues, would it be with our rights or the rules of the forum to start "naming and shaming" the venues that have dodgy supplies and such like.




I've discussed it with Ian, and as you probably suspected, the word is no. It's just too risky if someone doesn't get their facts straight (accidentally or even deliberately), or the venue improves and the thread isn't updated. It would leave SOS open to being sued, and that really wouldn't be a good idea.

So, sorry. But no. I think the best course of action would simply be to bring any venue with poorly maintained electrical supplies to the attention of the appropriate regulatory bodies -- the local council or the HSE.

Hugh




Indeed - it's not a magazine's job to police electrical safety in the field.
It would be about like witnessing an accident and phoning your local newspaper about it instead of dialling 999 for an ambulance.
If someone does report electrical problems promptly to the local council or HSE, then those bodies should fairly swiftly see that they are dealt with in any case, so the problem should not exist for very much longer.

--------------------
~~~ A weasel hath not such a deal of spleen as you are tossed with! www.feline1.co.uk ~~~


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
chris...
active member


Joined: 12/03/03
Posts: 4152
Loc: Glasgow
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #800134 - 02/01/10 05:06 PM
OK, so whilst rehearsing today, bass player experienced mild shock from mic. So we plugged the socket tester into the "garden" mains extension lead his bass combo was plugged into. Earth missing. Opened up the extension lead's plug and socket, expecting to find a loose/damaged earth connection. But no...

It was 2-core mains cable. Never had an of earth any kind (!)

Is this sort of thing common ? Are all lawnmowers double-insulated, or something ?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: chris...]
      #800150 - 02/01/10 06:20 PM
Quote Chris Edwards:


It was 2-core mains cable. Never had an of earth any kind (!)
Is this sort of thing common ? Are all lawnmowers double-insulated, or something ?




Basically, yes!

There are electrical safety "issues" with taking the earth outside the building due to the way most domestic supplies in the UK are earthed.

Due to this most garden appliances are double insulated and most have 2 core cables. I am however shocked (SORRY!) to discover that an extension cable (presumably with a 13A socket on the end) is being supplied wired with 2 core.

You do find 2 core cables made for garden use with lawnmower connectors on them (which are inherently 2 pin), and I hope that lethal extension came from some numpty modifying such a lead rather then being a commercial product.

When powering outdoor gigs from a building supply which is suspected to be TN-C-S or (PME) connected (the normal way these days), the safest way to do it is to bring out the live and neutral and derive a TT supply locally (with an RCD and local earth connection) or to use an isolating transformer (with local spike) and derive a TN-S supply with your own transformer.

Both require some thought and some specialist tools to test and verify for safety, and the issue is largely ignored by a lot of folks, but there is a right way and a wrong way to do these things.....

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
chris...
active member


Joined: 12/03/03
Posts: 4152
Loc: Glasgow
Re: Well, yeah, again, electric shocks from mics !! new [Re: dmills]
      #800157 - 02/01/10 06:42 PM
Quote dmills:

most garden appliances are double insulated and most have 2 core cables.




Ah, right.


Quote:

I am however shocked (SORRY!) to discover that an extension cable (presumably with a 13A socket on the end) is being supplied wired with 2 core.

You do find 2 core cables made for garden use with lawnmower connectors on them (which are inherently 2 pin), and I hope that lethal extension came from some numpty modifying such a lead rather then being a commercial product.




I'm not familiar with this 2-pin lawnmower connector. My own tiny flymo simply has a regular 3-pin mains plug.

Anyway, back to the extension lead in question. Yes, it had a 13A 3-pin mains plug at one end, and a 3-pin socket on the other. The bass player remembers buying it from B&Q some years ago - ie. not modified by a numpty...

This experience made me wonder if such extensions (2-core mains cable, with 3-pin plug/socket) are common in the gardening fraternity - with the understanding they're only to be used with double-insulated kit.

But I take it you're confirming this is not the case ?

Ta

PS - incase I wasn't very clear, this was an indoor rehearsal. The "garden" extension simply came to hand easily.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: chris...]
      #800159 - 02/01/10 06:56 PM
Quote Chris Edwards:


But I take it you're confirming this is not the case ?





Indeed, anything with a 13A socket on it (with very few specialist exceptions (of which an extension lead is never one)), should have a earth connection.

This is the sort of thing that begets two core cables for garden use:
http://www.maplin.co.uk/Module.aspx?moduleno=13176

Note that a two core cable with a 13A PLUG on one end and a female one of these on the other is totally standard (and safe) as a cable for things like some flymo lawnmowers. What you should never see is such a cable with a SOCKET on it.

I would suspect someone of modifying a lawnmower cable, but I suppose anything is possible.

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
chris...
active member


Joined: 12/03/03
Posts: 4152
Loc: Glasgow
Re: Well, yeah, again, electric shocks from mics !! new [Re: dmills]
      #800166 - 02/01/10 07:13 PM
Quote dmills:

Indeed, anything with a 13A socket on it (with very few specialist exceptions (of which an extension lead is never one)), should have a earth connection.



Right!


Quote:

This is the sort of thing that begets two core cables for garden use:
http://www.maplin.co.uk/Module.aspx?moduleno=13176

Note that a two core cable with a 13A PLUG on one end and a female one of these on the other is totally standard (and safe) as a cable for things like some flymo lawnmowers.



Yep - makes sense.


Quote:

What you should never see is such a cable with a SOCKET on it.




Yep - understood.



Quote:

I would suspect someone of modifying a lawnmower cable, but I suppose anything is possible.




As I said, he has no recollection of modifying this extension - but I'll check again...

Thanks for your help!

Chris


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
adamb1026



Joined: 05/10/09
Posts: 60
Loc: Belfast, N.Ireland
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #803202 - 13/01/10 01:36 PM
Hey guys,

been a while since I've been on here, thought I would keep you updated.

So far so good! No shocks in any venues...yet! Bought the Maplin plug tester and found one of my 4 way adapters had no earth! . Bit red faced when I saw only two lights

Checked the guitarists plugs and the venues, all of which so far are in good order.

Here's hoping it continues

Thanks again guys for all of your help


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
plodsmeade



Joined: 03/01/06
Posts: 61
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #834561 - 19/05/10 05:19 PM
Quote Hugh Robjohns:


If one or other of those mains safety earths becomes high resistance or disconnected, then the mains input filtering of the amp or mixer will tend to pull everything connected to the now disconnected earth line up to half mains volts (115V in the UK and Europe).





I'm not sure I fully understand how the 115V float works, in so far as what's going on in the device?

Is it something like the voltage is +/- 115V relative to ground only (giving the device the 230V range in use)?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: plodsmeade]
      #834572 - 19/05/10 06:03 PM
It's usually capacitors connected between the live and neutral and the earth. Without an earth reference, it'll float up to a point halfway between the L and N terminals i.e. 115v.

You can see the same phenomenon on class II equipment like DVD players that employ similar filtering. If you measure the potential of the case with respect to a good earth, it'll be in the region of 115v. It's quite safe to touch as there's no significant amount of current available to do you any damage. If you connect a lot of class II equipment together though, you can sometimes feel a bit of a tingle...

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: plodsmeade]
      #834602 - 19/05/10 08:39 PM
Quote plodsmeade:

Is it something like the voltage is +/- 115V relative to ground only (giving the device the 230V range in use)?




No. That arrangement would be 'balanced mains' which brings with it a whole host of other issues -- both good and bad.

In general, single phase mains supplies operated as an unbalanced system. The neutral is tied to the earth (ground) and the live carries (in Europe) 130V AC relative to that.

To help get rid of any nasty high frequency rubbish on the supply lines, it is common practice, as Sheriton says, to employ bypass capacitors between the live-earth and neutral-earth. That way, any high frequency rubbish gets passed straight into the earth line and away from the equipment.

However, if the equipment safety earth is missing because of a miswired plug or other fault, or if it is a class II (double isulated) device, then what would have been the earthed point of the capacitor interconnection gets dragged up to half the total voltage across both capacitors -- 115V in Europe.

Again, as Sheriton says, the size of the capacitors and the impedance of the supply lines means that no appreciable current is likely to flow..... but if you have several devices all sitting across the mains, each passing some current, then there can be sufficient to give a nasty tingle if not a lethal belt.

With normal mains-earthed equipment, shocks from the metal work are an obvious and definite indication of a serious fault. With Class II devices, it shouldn't happen, but it can and it doesn't necesarily indicate a fault... but is certainly annoying.

Thankfully, it is easily fixed by providng a proper safety earth and a lot of equipment is designed with this option in mind.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
plodsmeade



Joined: 03/01/06
Posts: 61
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #834798 - 20/05/10 03:49 PM
thank you both, that seems to make sense.

so the 115V is relative to earth, so touching anything earthed is likely to cause a shock, such as a radiator or earthed casing on another unit, not just the mic-mixer-earth?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: plodsmeade]
      #834883 - 20/05/10 09:24 PM
Quote plodsmeade:



...so the 115V is relative to earth, so touching anything earthed is likely to cause a shock, such as a radiator or earthed casing on another unit, not just the mic-mixer-earth?




No, as the earth conductor is not connected to the supply-earth, only things connected to your equipment or metal casing, guitar bridge, strings, etc will rise to this voltage.

Real problem is if there is a serious live to casing fauly on your gear while the earth conductor is compromised -then it's not uncomfortable, it's lethal!

>

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: plodsmeade]
      #834927 - 21/05/10 08:15 AM
Quote plodsmeade:

so the 115V is relative to earth




Yes. I think Nathan may have misunerstood what you meant.

Quote:

so touching anything earthed is likely to cause a shock, such as a radiator or earthed casing on another unit, not just the mic-mixer-earth?




Yes. Because your body then forms a circuit between the case which is floating at 115V, real earth, the earthed neutral at the substation and back to the box.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #835224 - 23/05/10 10:10 AM
Yes, I agree Hugh, I think I got the wrong end of the stick there...

>

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Lalala Music



Joined: 26/07/10
Posts: 22
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #848774 - 26/07/10 08:42 AM
Ahh the electric shock issue! Have had that a couple of times before. I'm a guitarist and singer for Her Sweet Suicide, and had these shocks a while back. My rig mainly consists of an unearthed POD Live... so you can already figure out where the shocks are coming from. I am merely conducting some form of electricity to the mic by touching the guitar, and well, I'm then getting shocked on my lips. That's one hell of a kiss of death!

Solution: Bought an extension cord which had a third earth prong! All good now!

Cheers,
Patrick

--------------------
Hi my name is Patrick. I run Lalala Music an online music business plan to help musicians create, promote, distribute and perform their music.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Nathan



Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
Re: Well, yeah, again, electric shocks from mics !! new [Re: Lalala Music]
      #849270 - 27/07/10 07:24 AM
I take it that you Pod Live is not double insulated, ie it needs its earth connection.

>

--------------------
planet nine
lincoln, uk.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
damoore



Joined: 05/07/09
Posts: 326
Loc: New Hampshire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Statick]
      #856025 - 24/08/10 01:03 AM
Quote Statick:



so the moral is, i guess, test all the extensions as well, especially if it's venue-owned gear and not your own.




Saw this once in an amusing way. Well, it seems amusing now. Was working late and the cleaners were vacuuming. A cleaner got in the lift and went upstairs but only half her extension cord went with her. She got half a flight up and the cord caught on the doors and the lift came to a shuddering halt. We couldn't get it to go down again so I got the office tool kit and removed the plug so the cord would slide through the doors and the lift would continue to the next floor.

After we retrieved the cleaner and the cord I looked at it intending to reconnect it and thought to check the far end. Turned out the other end was miswired! No idea if the end I had taken apart had been miswired the same way. At that point I refused to put it back together. I was kind of spooked - if I had just gone ahead and connected it up "properly" I would have unwittingly produced a cross-wired extension cable.

Moral is it does matter that the cable is correctly connected at both ends. Just having three random wires make the correct connections is not good enough. That and don't assume the previous guy did it right.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
martin randle
member


Joined: 03/03/00
Posts: 246
Loc: cambridge uk
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #950359 - 30/10/11 09:19 PM
This same thing happened to me last night (shock off the mic) all the gear we were using (PA mixer guitar amps keyboards were running off one double socket via extension leads. I only use the same leads and have never experienced this before - however we have never played at this venue before.

my girlfriend came up with a classically simple idea and went to my car and came back 2 minutes later with my rubber floor mats. I stood on these all night and didn't get another shock.

I will get a circuit tester before I play there again.

(The Social Club Witchford Ely Cambs UK)

--------------------
http://www.myspace.com/cottonsalamander


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
TSH-Tim



Joined: 21/02/11
Posts: 816
Loc: Guildford
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #950363 - 30/10/11 09:37 PM
Buy yourself a plug tester (£3.50 from CPC)

--------------------
PA Hire Surrey
Lighting Hire Surrey


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: TSH-Tim]
      #950446 - 31/10/11 01:20 PM
Yes -- I would stringly advise NEVER plugging anything into a wall socket until you've tested it with a simple mains-tester plug. I've come across way too any pubs, clubs and conference venues with missing earths and L-N reversals.

Also, once you've tested the socket and you know it is safe, ALWAYS plug the equipment in via RCDs, just to make absolutely sure!

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Gary_W



Joined: 18/10/06
Posts: 376
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993390 - 18/06/12 01:34 PM
I'd like to thank everyone for the info in this thread - I need to find the culprit of a tingle here.

I've played live twice over the last 3 weeks. At both venues, I've had shocks to the lips. I play guitar and sing, though in this band I'm not singing often.... Just as well. It was a mild tingle at venue #1 and sparks, noise and pain at venue #2..... It was too much to be DC - the culprit felt like a reasonably high potential difference between my guitar bridge and the microphone. Interesting to read here about the float up to 115v as this seems to make sense. This was not 'tongue on a 9v battery' - rather more impressive unless I'm being a complete fairy.... Fortunately our bass player had one of the mic pop shields of the hair bear bunch variety which provided ample insulation (no, I am not suggesting this as a solution to my problem before anyone gets excited but this obviously stopped the issue of sparky lips )

I will double check it tonight, but I actually tested the earth bonding on my amp a few weeks back (I had a friend test it to medical grade standards which tested earth bonding, mains leakage, the works and it's spot on and as an owner of a multimeter I'm no stranger to keeping myself alive!). I may have swapped mains leads but all of my mains leads are in good condition so I'll be surprised if it's that. But multimeter from earth to my guitar bridge will be the first thing I do just to rule out that bit.

One question here - folks are mentioning double insulated equipment potentially having a potential...... On my pedalboard, I have several pedals run from a 9v power supply - I can't see how it can be them (if my guitar earth is indeed good as suspected then 9v to earth is just going to drag the 1700mA supply down isn't it?). I also have a couple of Carl Martin pedals (a Quattro and a chorus). These have 2 core mains going to them and are both double insulated. So could it be one of them?

Can anyone tell me a bit more about this double insulated upping the earth potential thing or have I misunderstood? Obviously I'll test tonight with just amp and guitar and then add the pedalboard back in. I'm hoping for no issues at my end which leads me to external problems (venue / pa / extension leads).

On the two occasions it happened it was 2 different venues and 2 different PA's. One thing that was common was a few extension leads (provided by another band member). So, unless we have 2 dodgy PA's and 2 dodgy venues then the extensions are likely culprits are they not?

Thanks

Gary


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Gary_W



Joined: 18/10/06
Posts: 376
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993466 - 18/06/12 07:23 PM
OK, I've tested my gear out and all appears fine.... I have a good earth to my amplifier and this continues on to the bridge of my guitar. With the pedal board in, it adds about 2 ohms of resistance (according to my meter whose tollerence is not great).

In short, I have under 3 ohms between my guitar bridge and the house wiring according to the aforementioned cheapo meter. So it's OK in my opinion but correct me if you disagree

I also tested for AC and DC voltage. Unsurprisingly with a decent earth, there was none.

So if I am properly earthed on the guitar side of things, the posibilities are:-

1. Broken earth in the extension lead supplying my guitar kit
2. Broken earth at two different venues (possible but less likely)
3. Broken earth on two seperate mixers (again less likely)

So favourite culprit is option 1 in my opinion - any advance on that?

Many thanks

Gary


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Gary_W]
      #993482 - 18/06/12 08:59 PM
My vote is for a dodgy mains extension. Best advice if you want to live is (a) never use someone's else's mains extensions and (b) ALWAYS test every wall socket and mains extension socket with a pukka mains tester before you use them!

It's disturbingly common to find wall sockets with dodgy earths, so please do check. But given the common factor of a mains extension I think you would be well advised to get that checked pronto!

Regarding the double-insulated pedals, they are grounded through the guitar amp, which you have proven is properly grounded when plugged into a decent grounded mains outlet.

To sum up, my advice would be (1) to buy a simple plug-in mains socket tester and use it on every wall socket and mains extension every time you rig your gear; (2) invest in a plug-in RCD unit for your gear--it will save your life should the worst happen with a dodgy earth somewhere; (3) get those mains extensions tested and repaired as a matte of urgency.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Gary_W



Joined: 18/10/06
Posts: 376
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993511 - 19/06/12 07:40 AM
Thanks Hugh - I really appreciate the advice. I will invest in a socket tester and ensure I take my own extension lead.

It's clear that my guitar earth is at earth potential (where it should be) and that my zapping here came from something else - at the first gig, I was straight into a socket but this time I was using an extension.

Whilst I can avoid my guitar ground floating up by socket tester + own good extension lead, I can still get in trouble if the mixer has a floaty ground can't I? So we're talking about the scenario where it really is the mic giving the shock, not the mic being the decent earth (as seems to mostly be the case here). So unless I become 'band electrician' I'm still stuffed BECAUSE I've got a good earth on my own kit.....


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Gary_W]
      #993524 - 19/06/12 09:05 AM
Quote Gary_W:

Whilst I can avoid my guitar ground floating up by socket tester + own good extension lead, I can still get in trouble if the mixer has a floaty ground can't I? So we're talking about the scenario where it really is the mic giving the shock, not the mic being the decent earth (as seems to mostly be the case here). So unless I become 'band electrician' I'm still stuffed BECAUSE I've got a good earth on my own kit.....




Yes, there are two ways of getting electocuted in this kind of situation!

The first is where the mic is properly earthed bu the guitar goes live, and the second is wher the mic goes live but the guitar is earthed. In both cases your body closes the circuit.

The good news is that unless there is a really serious fault somewhere, the mic is unlikely to reach full mains voltage. Worst case is that it might 'float' up to half-mains voltage (115V in the UK) if the PA equipment is ungrounded, and that would be from a relatively high impednace, so while unpleasant it's unlikely to be lethal. But it is an extremely unlikely situation in the first place since all power amps are class 1 devices (afaik) and they would impose a solid safety ground on the PA system anyway.

The only totally safe solution that protects you regardless of where the earth goes missing, is to always power your equipment via a good quality RCD. That way, if some of the mains current from either system ends up going somewhere it shouldn't via you, it will trup the power before it can do any serious damage.

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Gary_W



Joined: 18/10/06
Posts: 376
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993552 - 19/06/12 12:20 PM
Thanks again, Hugh

With regard to RCD's, it's all very well protecting my equipment (and I'll ensure I do so) but this still won't protect me from a dodgy mixer (for example) that has been brought and set up by someone else will it? As my guitar is well grounded, if my RCD detects current to earth it'll trip out MY RCD. As the offending live part is the microphone here which is coming from a mixer I'm not better off as that will keep going and passing me the juice!!

It's one of those situations where it's a very necessary conversation for a guitar player / bassist as you have both hands on a perfect earth connection. As such, you are at the mercy of other folks equipment / venue wiring more than most band members. You are in the position of being worse off if your kit IS perfectly grounded if someone else's is not!

I think I need a chat....


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: Gary_W]
      #993558 - 19/06/12 01:07 PM
Quote Gary_W:

As my guitar is well grounded, if my RCD detects current to earth it'll trip out MY RCD.




Note quite. Your RCD will only trip if it detects an imbalance between the live and neutral currents flowing through your own kit; it doesn't measure current flowing through the earth connection. So it won't trip if you're getting zapped by someone else's faulty kit. On the plus side, that does give you an indication of where the stray current is coming from - if your RCD hasn't tripped, it's probably not coming from your mains supply.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Gary_W]
      #993579 - 19/06/12 02:36 PM
You're right -- if the PA system is live and grounding via your system your RCD won't help because it won't interrupt the ground -- but it might still trip if it senses an imbalance of current on the supply.

If you have any doubts about the PA system, look for the PAT stickers -- ask to see the PAT records. Check if they are running their gear through RCDs... and if in doubt, be careful not to touch anything metallic!

And if you do detect anything that you're not happy about, make sure you get those responsible for the kit to investigate properly.

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Gary_W



Joined: 18/10/06
Posts: 376
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993659 - 20/06/12 06:33 AM
Thank you both - eBay socket tester is in the post and I will be multimetering the rest of the bands extension leads. Also going to take my DMV to the next venue so as, if anything daft DOES happen I can get a bit more buy-in from everyone..... If it says there is voltage it then makes it a lot more believable vs folks thinking I'm wearing nylon


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Jorge
member


Joined: 13/12/03
Posts: 324
Loc: New York, NY
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993663 - 20/06/12 07:45 AM
I don't know how common this is, either in the US or UK, but the subject of Reverse Polarity Bootleg Ground wiring in venues has been discussed on another forum. RPBG is one possible explanation for electric shocks from mics, and could potentially lead to fatal shocks.

I know nothing about electrical wiring in the UK, but for US 120 v three conductor circuits, a Bootleg Ground is when, if no true ground is available, the outlet neutral is connected to the outlet ground. This in itself is not usually a problem. Occasionally, however, on top of the Bootleg Ground miswiring, the building neutral is mistakenly switched with the building hot (Reverse Polarity). When what is thought to be the building hot and neutral leads are then connected to the outlet hot and neutral leads, respectively, what actually occurs is that the building hot is connected to the outlet neutral and the outlet ground (RPBG). This, unlike simple Reverse Polarity, or a simple Bootleg Ground, can cause the case and ground of devices (eg, mixer chassis, mic, guitar strings) to be at live potential. Not a problem until a person touches both that and an actual ground. Then (and this would happen commonly) the person will get a shock, potentially at high voltage.
The problem is that your simple outlet ground tester will find most faults but completely misses the RPBG configuration. You need in addition a noncontact tester that will identify a hot wire without actual metal to metal contact or access to a true ground. Here is a video that explains a simple procedure to find RPBG wiring. A noncontact tester could also find a high voltage (>90 volts) hot chassis, guitar strings, mic cable or mic.

http://www.youtube.com/watch?v=iLk-6pvSlWg&feature=plcp


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Jorge]
      #993675 - 20/06/12 08:39 AM
Quote Jorge:

I don't know how common this is, either in the US or UK, but the subject of Reverse Polarity Bootleg Ground wiring in venues has been discussed on another forum.




It's a very scary bodge, but thankfully not likely to happen in the UK. I have heard of similar situations in other countries though!

The reason it is so prevalent in the US is because a lot of buildings are fed with what is, in effect, a balanced 230V mains feed with a centre neutral. Some sockets are then run from one side and centre neutral (giving the 115V supply), while other sockets are run from the other side and neutral. Devices that require a lot of power -- like washing machines and so on -- are often powered from the 240V supply directly.

The centre neutral is normally bonded to earth at some point to make the 115V supplies 'unbalanced' in the conventional way, and hence some electricians have been known to indulge in the lazy practice of using the neutral as a makeshift earth rather than run a proper earth cable to the mains sockets.

However, if things then get confused elsewhere in the building it is possible for the live and neutral wiring to end up being reversed, potentially resulting in equipment cases becoming live relative to a genuine earth (like the water pipes and CH radiators!).

In the UK, because we only have a 240V supply in domestic buildings, and because the IEE wiring regulations are so strict, we can't suffer the RPBG syndrome you describe for the US. It could potentially happen in buildings with 3-phase supplies, but again, the wiring regulations are so strict that it just won't happen.

Quote:

The problem is that your simple outlet ground tester will find most faults but completely misses the RPBG configuration. You need in addition a noncontact tester that will identify a hot wire without actual metal to metal contact or access to a true ground.




Yes... it would be a bit of a worry! For all it's faults, there are many good things about living in the UK!

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Dave Gate
active member


Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993702 - 20/06/12 09:32 AM
Many years ago, before the UK switched to the European standard for three phase colour coding (green for Earth, blue for neutral and brown/black/grey for the three lives) I was working on a show in what had been a reasonably famous venue (no names) where the three phase mains had to be tailed in by an electrician. Who attached the blue live phase cable to the neutral, and the black neutral cable to the live phase that should have had the blue cable.

Oh that was fun when the power went on

--------------------
Gear List: reverse only.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Jorge
member


Joined: 13/12/03
Posts: 324
Loc: New York, NY
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993754 - 20/06/12 02:17 PM
Thank you Hugh for that crystal clear explanation. Yes there are some downsides to the anti-regulatory ideology and/or poor enforcement of regulations that have become so prevalent in the US. The good news is no one I know has ever been electrocuted by an RPBG wiring configuration or anything else. Just to be safe, however, I have just ordered a noncontact tester and will add that to my wall outlet testing routine in the venues we play.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Dave Gate]
      #993757 - 20/06/12 02:19 PM
Quote Dave Gate:

Many years ago, before the UK switched to the European standard for three phase colour coding (green for Earth, blue for neutral and brown/black/grey for the three lives) I was working on a show in what had been a reasonably famous venue (no names) where the three phase mains had to be tailed in by an electrician. Who attached the blue live phase cable to the neutral, and the black neutral cable to the live phase that should have had the blue cable.

Oh that was fun when the power went on




Remind me never to touch UK/EU power. In the US the standard is Green = Ground, White = Neutral, and Red, Blue, Black for the three phases. Would be way to confusing.

I can't think of any place I have ever run across with hot swapped to ground and neutral on the hot for the record, scary thoughts there that that can even exist.

Hugh is correct on the basic wiring for most houses in the US (Commercial buildings tend to have true 3-phase though). But even in houses a fairly standard coloring is used, where there is not usually differentiation between phases, but rather the hot is usually black with neutral white and green ground. For 220v in the US Red and Black are usually hot and White is still Neutral with Green for Ground.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Dave Gate
active member


Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993761 - 20/06/12 03:24 PM
It used to be very confusing here, which is where the offending electrician went wrong. Three phase mains had Earth = green, Neutral = black, Red/Blue/Yellow = 3 x live; but single phase had Earth = green & yellow, Neutral = blue, Live = brown.

This is one area where we can wholeheartedly thank the EU for imposing a standardisation . . .

--------------------
Gear List: reverse only.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Dave Gate]
      #993859 - 21/06/12 09:21 AM
Three phase power isn't something I get to play with these days, but when I did it was red, blue, and yellow and I think if I was presented with brown, black, gey cables today I'd be scratching my head with them!

The definition of a competent person is someone who knows when they don't know enough, and stands back to let someone better trained take over!

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Dave Gate
active member


Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #993871 - 21/06/12 09:47 AM
I was there at the changeover, and had to get my venue's old Red/Blue/Yellow Camlock outlets and cables converted to Brown/Black/Grey Powerloks. But the new colours make more sense, as the earth, neutral and first live phase are in line with what you'd find in a single phase UK mains plug.

--------------------
Gear List: reverse only.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Dave Gate]
      #993906 - 21/06/12 11:08 AM
I agree it makes sense in the wider construct -- but red, blue and yellow, all being bright colours, shouted 'live' to me. Brown black and grey are all pretty earthly colours....

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Dave Gate
active member


Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #993908 - 21/06/12 11:13 AM
That sounds like the old UK wiring system (before my time!) where red was live and black was neutral (can't remember what earth was). You still find that in domestic wiring behind the sockets and switches, with the earth usually being an unshielded core (which most sensible people slip a green and yellow sheath over!). If you've ever changed a socket or a lightswitch you'll know what I mean.

--------------------
Gear List: reverse only.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Raphbass



Joined: 30/12/06
Posts: 228
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #997166 - 11/07/12 10:58 AM
On a gig last Saturday, the guitarist plugged into a different socket to the rest of us - there was what felt like a good 100+ voltsAC between his strings and his mic that was going into the PA. When he first mentioned it I thought he meant the common little static "zap" you sometimes get - I didn't realize till I myself touched his strings and the mic at the same time that it was a serious buzz - I remember from messing about with transformers as a kid what 120V AC feels like, this was similar.

I got him to plug into a plugboard on the same wall socket as the rest of us and the problem was solved. Not sure whether I should have informed the venue that there was an issue between two earths in different sockets in the same room - or is this normal?

I assume that for example if they plug in two brass standard lamps or similar, one on each wall socket, that the guy holding both would be getting a good dose of current and if the two lamps came into contact there would be a shower of sparks between them.

I've always assumed that earth is earth is earth - I don't quite get how two earths can be so many volts apart, unless something's gone terribly wrong with the building's wiring. This is a posh modern hotel by the way, not a crumbling third-world establishment (and I've seen a few!).


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Raphbass



Joined: 30/12/06
Posts: 228
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #997170 - 11/07/12 11:08 AM
PS - re colours - yes, brown seems to me the most earthly of all colours, how that got to be "live" totally beats me. And given that a common symptom of colour blindness is to confuse green and brown it seems mental to have the two close together in a mains plug. What was wrong with red for live?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Raphbass]
      #997177 - 11/07/12 11:18 AM
Quote Raphbass:

On a gig last Saturday, the guitarist plugged into a different socket to the rest of us - there was what felt like a good 100+ voltsAC between his strings and his mic that was going into the PA. When he first mentioned it I thought he meant the common little static "zap" you sometimes get - I didn't realize till I myself touched his strings and the mic at the same time that it was a serious buzz - I remember from messing about with transformers as a kid what 120V AC feels like, this was similar.




If it was a true shock from incorrect grounding that indicates two things. First that the socket ground was a much higher impedance than it should be(Bad connection) or missing(No connection). And that there was likely a fault inside of the guitar amp that needs to be checked out.

Quote:


I got him to plug into a plugboard on the same wall socket as the rest of us and the problem was solved. Not sure whether I should have informed the venue that there was an issue between two earths in different sockets in the same room - or is this normal?





Yes they need to be informed.

Quote:


I assume that for example if they plug in two brass standard lamps or similar, one on each wall socket, that the guy holding both would be getting a good dose of current and if the two lamps came into contact there would be a shower of sparks between them.





Not unless there was some VERY bad wiring in the venue, or there is a fault in the lamp attached to the socket with the bad ground.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Dave Gate
active member


Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
Re: Well, yeah, again, electric shocks from mics !! new [Re: Raphbass]
      #997195 - 11/07/12 12:08 PM
Quote Raphbass:

PS - re colours - yes, brown seems to me the most earthly of all colours, how that got to be "live" totally beats me. And given that a common symptom of colour blindness is to confuse green and brown it seems mental to have the two close together in a mains plug. What was wrong with red for live?




For domestic use it's supposed to be green and yellow striped. So, for colour-blind people you have a dark colour, a light colour and stripes. Not sure how effective it is, though.

--------------------
Gear List: reverse only.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #997316 - 11/07/12 10:30 PM
Red/Green/Black was replaced for flexible cables many years ago precisely because of the problem of red/green colour blindness (Back when appliances commonly came without plugs), a red/green reverse in the plug would leave the case live, and this was in the days before RCDs!

This left us with the interestingly odd situation in that single phase flexible cables were brown/blue/green-yellow, three phase flexible cables were usually brown/black/grey with a blue neutral and the usual striped earth (EU standard).
Fixed installation wiring however was usually red/black/green-yellow for single phase or red/blue/green-yellow/black(neutral) for three phase (Note that blue means different things depending on whether the wiring is a flex(Neutral) or installation(Phase)). Note also that a single phase circuit fed from any phase was usually red/black.....

Anyway all this got harmonised across Europe with the new scheme being brown/blue for single phase circuits, black/brown/grey + blue neutral for three phase, this is the same for both fixed install wiring and flexible circuits. It caused some few problems (and a very few expensive mistakes) when first introduced, but the fact that in a modern install blue has only one possible meaning (neutral) is on aggregate a net win.

The only striped wire in common use for mains voltage is the green/yellow one that is only ever used for earth connections and is two colours precisely so that no matter what colour vision problems you have it is obvious.

That concludes a short history of UK wiring.

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Raphbass



Joined: 30/12/06
Posts: 228
Re: Well, yeah, again, electric shocks from mics !! new [Re: seablade]
      #998192 - 16/07/12 05:28 PM
Quote seablade:

Quote Raphbass:

On a gig last Saturday, the guitarist plugged into a different socket to the rest of us - there was what felt like a good 100+ voltsAC between his strings and his mic that was going into the PA. When he first mentioned it I thought he meant the common little static "zap" you sometimes get - I didn't realize till I myself touched his strings and the mic at the same time that it was a serious buzz - I remember from messing about with transformers as a kid what 120V AC feels like, this was similar.




If it was a true shock from incorrect grounding that indicates two things. First that the socket ground was a much higher impedance than it should be(Bad connection) or missing(No connection). And that there was likely a fault inside of the guitar amp that needs to be checked out.

Quote:


I got him to plug into a plugboard on the same wall socket as the rest of us and the problem was solved. Not sure whether I should have informed the venue that there was an issue between two earths in different sockets in the same room - or is this normal?





Yes they need to be informed.

Quote:


I assume that for example if they plug in two brass standard lamps or similar, one on each wall socket, that the guy holding both would be getting a good dose of current and if the two lamps came into contact there would be a shower of sparks between them.





Not unless there was some VERY bad wiring in the venue, or there is a fault in the lamp attached to the socket with the bad ground.

Seablade




Well yes there was a comedy moment as I looked at his 20yr-old Fender amp and he sort of took umbrage and said with a dry hint of confrontation "never had a problem before", and he then looked just as implicatingly (if that's a word!) at my mixer which is less than a year old, and PAT tested fairly recently... and there we stood for a few seconds in a stalemate. [Cue soundtrack to "the Good the Bad and the Ugly"]

In retrospect, I feel pretty pathetic that it didn't occur to me to get out the mains tester I have in my kit.

If there's a fault in the mains of one of the circuits, couldn't it render the earth live even without a fault in the gear? Haven't thought it through (and unlikely to bother!) but it seems it can't be a simple reversal of live and neutral as the amp was working fine, and the rogue voltage was a lot less than mains (about half I reckon).

Anyway I've emailed the venue to suggest they should check what's going on in their mains sockets.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Raphbass



Joined: 30/12/06
Posts: 228
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1000502 - 29/07/12 11:30 PM
Had a reply from the venue - apparently no fault with their sockets. I'm not going to bother asking what exactly they tested but will take their word for it. I could maybe get my stuff tested again or just leave it at that.

The guitarist is a sort of "rocker" type, very nice guy but exudes the vibe that he won't remain that way if riled - he insisted on the day that his amp was fine and who am I to suggest otherwise.

So the mystery remains - an AC voltage between two supposed earths, cured by plugging into the same wall socket. Weird.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Raphbass]
      #1000511 - 30/07/12 01:27 AM
Quote Raphbass:

Had a reply from the venue - apparently no fault with their sockets. I'm not going to bother asking what exactly they tested but will take their word for it. I could maybe get my stuff tested again or just leave it at that.

The guitarist is a sort of "rocker" type, very nice guy but exudes the vibe that he won't remain that way if riled - he insisted on the day that his amp was fine and who am I to suggest otherwise.

So the mystery remains - an AC voltage between two supposed earths, cured by plugging into the same wall socket. Weird.




I would strongly suggest if you work with that guitarist again, taking a look at the ground and making sure it is properly connected all the way through, and making sure you check the venue wiring yourself if you are ever there again. A 3 prong outlet tester at a minimum, but doing a full check with a multimeter isn't a bad idea, since you will want that to ensure ground continuity as well.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Raphbass]
      #1000533 - 30/07/12 09:37 AM
Quote Raphbass:

The guitarist is a sort of "rocker" type, very nice guy but exudes the vibe that he won't remain that way if riled - he insisted on the day that his amp was fine and who am I to suggest otherwise.




Potentially the bloke that might save his life!

Quote:

So the mystery remains - an AC voltage between two supposed earths, cured by plugging into the same wall socket. Weird.




Not weird, dangerous, and still in need of resolution.

hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Raphbass



Joined: 30/12/06
Posts: 228
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1000651 - 30/07/12 06:44 PM
Well - there was also the issue that there was no problem when he plugged into the same circuit as us. If his amp's casing/earth were live it would still be giving us shocks regardless which circuit it was on.

Sounds like the same issue as the OP - cured when everybody goes into the same socket. Trouble is, what I didn't mention is we blew the fuse at the end of one tune - you know, Standard 12/8 Blues Ending no.2 - "da, da-da, da-da, da-da, da-da .(drum fill) . da, POP!" - only cymbals ringing and an uncertain sax note hanging on, and of course darkness as the lights went out (LEDS, 100W total at the most so can't be blamed).

Next time two extensions, even if going from adjacent sockets.

The operations manager at the venue just said briefly "no fault was found". I don't know what else I can do, I'm responsible for my gear, he's responsible for his hotel.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Raphbass]
      #1000688 - 30/07/12 10:45 PM
Quote Raphbass:

Well - there was also the issue that there was no problem when he plugged into the same circuit as us. If his amp's casing/earth were live it would still be giving us shocks regardless which circuit it was on.





No it wouldn't. If the ground is correct and the case becomes live due to a fault in the amp, it drains to ground through the ground wire, not through the person to ground.

NOTE: There are TWO seperate faults in this type of situation. And either without the other won't show symptoms.

Quote:


The operations manager at the venue just said briefly "no fault was found". I don't know what else I can do, I'm responsible for my gear, he's responsible for his hotel.




You are responsible for safety as well in operation of your equipment. If you go back to the venue you really should consider it your responsibility to make sure that what you are plugging into is in fact safe. Again a 3 prong tester at a minimum, but a multimeter to test not only the socket but also the amp and kill two birds with one stone.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Raphbass



Joined: 30/12/06
Posts: 228
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1000786 - 31/07/12 09:40 AM
Yes - if I do another gig at that venue, knowing I've had a problem in the past, I would see it as my responsibility, not to mention self-interest, to check everything including their sockets.

Meanwhile though, if someone at the venue gets electrocuted and they look at emails mentioning the issue, my email might be part of the evidence but I can't imagine they'll come after me as being responsible by negligence.

If you warn someone there's a frayed brake hose on their car and they say "no it's fine" and drive off, I doubt very much you could be sued for their subsequent death.

By the way - what is an acceptable resistance between the AC plug earth and the ground pin at the end of the mic lead?

I just pulled out a random mic lead and it's about 0.8ohms, but from AC plug through the mixer to mic lead it's around 3ohms. Is this normal?


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Raphbass]
      #1000814 - 31/07/12 11:18 AM
Quote Raphbass:


Meanwhile though, if someone at the venue gets electrocuted and they look at emails mentioning the issue, my email might be part of the evidence but I can't imagine they'll come after me as being responsible by negligence.

If you warn someone there's a frayed brake hose on their car and they say "no it's fine" and drive off, I doubt very much you could be sued for their subsequent death.





No in that case you have done what you can I agree. It is not your responsibility to go in and check everything for them when you are not there so long as you have notified them. Then it becomes their responsibility to ensure their venue is safe.

Quote:


By the way - what is an acceptable resistance between the AC plug earth and the ground pin at the end of the mic lead?

I just pulled out a random mic lead and it's about 0.8ohms, but from AC plug through the mixer to mic lead it's around 3ohms. Is this normal?




Both of those should be fine, however it is far more important the resistance between AC ground and the chassis of the equipment, not the ground of the mic cable. In general both of these will be connected yes, but it doesn't always happen, and is possible for the ac ground and signal ground to be connected without either going to the chassis which is still an issue.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Raphbass



Joined: 30/12/06
Posts: 228
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1000834 - 31/07/12 11:51 AM
Just wiggling the mains connector in the IEC socket at the back of the mixer has achieved a reliable 1.2 ohms now, from the AC plug earth to the mic lead and to the casing. Maybe a bit of switch cleaner on contacts would be in order.

When I next play with the same guitarist should I check continuity of his AC earth to the guitar bridge? I'll probably be doing it under a stony scowl!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Raphbass]
      #1000860 - 31/07/12 12:30 PM
Quote Raphbass:


When I next play with the same guitarist should I check continuity of his AC earth to the guitar bridge? I'll probably be doing it under a stony scowl!




AC Earth to the interior chassis of the amp itself. Remember, the AC earth is there as a safety against a fault of the amp taking the chassis live, which the electricity will then try to find the nearest path to ground. If the AC earth is not there, then there is no path to ground and noone gets hurt, until it is provided through a human being. The most common way this happens is a guitarist that is plugged into this amp that the chassis is now live on, places his fingers on the strings of his guitar and then steps up to a microphone connected to a properly grounded audio system. He has then provided a closed path to ground, through himself, to the audio system's AC ground, and this is how very bad things happen and guitarists get killed, but not the only way. Another way I have heard happening is the guitarist has a momentary contact with a grounded part of the building, for instance a radiator (Metal piping is usually grounded in buildings) while touching his strings which also completes the circuit.

Obviously you have to check to an area of the amp that is actually conductive, so look around the inputs especially for some steel. From what I have heard, I imagine all of this is part of the standard PAT test that must be done on your side of the pond on occasion, so I would look at the regulations for that for a good starting point as well (But hope someone on that side of the pond will come in to clarify, confirm, or correct me on that point).

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: Raphbass]
      #1000862 - 31/07/12 12:34 PM
Yes.

And if he scowls ask him whether he values his life or not?

Hugh

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dubbmann
active member


Joined: 17/03/04
Posts: 1404
Loc: 3rd stone from the sun.
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1000936 - 31/07/12 05:15 PM
hi all,
.
forgive if this q has been asked before but i don't understand if microphone shocks are a recurrent issue, why not switch to a wireless (battery powered) connection between mic and board? if the mic is not connected to an amp physically, it CAN NOT deliver a shock. break the metal connection, save the singer, it seems to me.

i also wonder if the same effect can be achieved using a wired mic going into an optical-transducer based compressor. not sure about that one.

anyway, thoughts?

d

--------------------
"Patsy had the drug tolerance of Keith Richards and the moral rectitude of Brian Jones." - Dr. Walter Bishop, "Fringe"


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: dubbmann]
      #1000953 - 31/07/12 06:12 PM
Quote dubbmann:

why not switch to a wireless (battery powered) connection between mic and board?




Mainly because wireless mics are (a) a lot more expensive and need wireless receivers, (b) they are noisier and use companding systems which can mistrack in some situations and degrade the sound quality noticeably, and (c) are prone to interference, fading, glitching etc, and (d) licence-free channels are notoriously unreliable in busy parts of the country, (e) licensed channels add to the expense.

But if you are prepared to invest in high quality licensed radio mic systems and spend the effort installing proper RX aerials it is a good solution.

Proper equipment PAT tests and sensible grounding procedures work perfectly well though!

Quote:

i also wonder if the same effect can be achieved using a wired mic going into an optical-transducer based compressor. not sure about that one.




No. The attenuating element is a light-dependent resistor, but the signal isn't optically-coupled or isolated. Grounding issues would remain, I'm afraid.

H

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: dubbmann]
      #1001001 - 31/07/12 10:56 PM
Quote dubbmann:

hi all,
.
forgive if this q has been asked before but i don't understand if microphone shocks are a recurrent issue, why not switch to a wireless (battery powered) connection between mic and board? if the mic is not connected to an amp physically, it CAN NOT deliver a shock. break the metal connection, save the singer, it seems to me.

i also wonder if the same effect can be achieved using a wired mic going into an optical-transducer based compressor. not sure about that one.

anyway, thoughts?

d




I am surprised Hugh didn't answer the most obvious thing, because this merely hides a symptom, not solves the problem. If this happens you still have at least TWO safety failures (A failure in the amp and the removal of a path to ground) and it is more than possible to kill a guitarist by more ways than them stepping up to the microphone, it is just that is the most common symptom of this. As I mentioned above anything they touch that is properly grounded will injure if not kill them by completing the path to ground through their bodies.

Again FIX THE PROBLEM. Don't hide the symptoms.

Seablade


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Sheriton



Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
Re: Well, yeah, again, electric shocks from mics !! new [Re: seablade]
      #1001338 - 02/08/12 11:50 AM
The title of this thread has been bugging me ever since its inception - as has been highlighted again and again, the mic is grounded and so is not causing the problem here. (Alright, in a small minority of cases it's possible that it could be a problem but the vast majority of cases involve a guitarist being at a high electrical potential because of a fault somewhere in their equipment and completing the circuit by touching the grounded mic.) Sorry Dubbmann but I'm right with Seablade here - sort out the underlying problem.

--------------------
There's nothing we can't face... Except for bunnies


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
seablade



Joined: 21/11/04
Posts: 3768
Re: Well, yeah, again, electric shocks from mics !! new [Re: Sheriton]
      #1001352 - 02/08/12 12:46 PM
Quote Sheriton:

The title of this thread has been bugging me ever since its inception




When this thread was stickified, it was the second of two threads on the topic in a short period of time. The first would have been a much better thread to stickify at the time, but I am happy at least one of them did get stickied.

Yes the title of the thread is misleading, and if a mod cared to modify it I certainly won't complain, but what I think is good about the title is that it clearly says the symptom in it, which means many people will see it and recognize it as the problem before posting another thread on it. However as has been pointed out, the symptoms are not the cause and that can be confusing unless you read the thread.

In the end, we should probably type up a single long article on the topic that summarizes all the basic concepts of how this happens, and see if that can replace this thread as a sticky. That was people need to read one post instead of an entire thread to understand why the suggestion above wasn't really a good one(No offense intended). This post by the way is not one:)


Quote:

...(Alright, in a small minority of cases it's possible that it could be a problem but the vast majority of cases involve a guitarist being at a high electrical potential because of a fault somewhere in their equipment and completing the circuit by touching the grounded mic.)...




I will also note that it isn't really just guitarists. When I started working full time in ministry, one of the first things I had to deal with was baptisms and how to mic those up. Obviously any electrical equipment near water is a touchy subject, but in the not to recent past before I came on there was a pastor that got electrocuted in the baptism pool when he reached up and grabbed a microphone to redirect it to him.

The first response of many people was along the lines of...

"That microphone had something called phantom power going to it, which when the pastor with his wet hands reached up to grab the mic, caused it to short circuit through his body, killing him."

As most people that understand how phantom power works would tell you, this is exceedingly unlikely and would generally require at least two body parts touching the microphone to even begin to contemplate, but even then is exceedingly unlikely. Much more likely would be that water gets inside the microphone, shorts out the microphone and destroys the microphone, long before anyone got injured.

Turns out what had happened is pretty much exactly what happens with guitarists. An AC ground was not connected. For guitarists, the reason we often see this is in some cases they will remove the AC ground to prevent a ground loop from ruining their sound, as often times people don't understand there are much safer ways to correct a ground loop, (Isolate the AUDIO ground instead of the AC ground). In the case of the baptismal however it was a much more basic issue.

Someone had built the water pump/heater at home and had not properly grounded it. In actuality what was happening was that every time that pastor stepped into the baptismal pool, they were stepping into an electrified pool of water. The issue was that electricity never had a path to ground so it did not endanger the pastor.... until he reached up and grabbed a path to ground, through the microphone into the properly designed and built sound system.

Let me repeat, in this case, just like in the case with guitars, the electrified problem already existed, electricity was going where it shouldn't have gone (The guitar amp, or the baptismal pool). The danger was that it also didn't have a SAFE path to ground (Water Pump/Heater was not properly grounded, Ground lead broken off Guitar Amp Plug, Ground Wire missing in Outlet, etc.) so it took the first path to ground it got, which in both of these cases tends to go through a human body.

Again there are at least two electrical faults occurring already in order for this to happen. First is that there is an internal fault causing the chassis to become electrified, and second is that there was no safe path to ground remaining that should have existed. At this point even if you could hide the symptoms, it is not very difficult for the electricity to take a different path to ground the next time someone touches something else that is grounded and the same result happens.

Seablade

EDIT:

This is why I WILL yell at you(Be you a professional or one of my students) if I ever see you use a 'cheater' plug (3-Wire to 2-Wire). You CAN use them correctly, most people do not. To use them correctly REQUIRES running a third wire between the cheater plug ground and a safe building ground. Guess what, you shouldn't EVER remove an AC ground.

And to be fair, it isn't just pastors or guitarists that cause this. I have literally walked into a venue while I was touring and been told I had to use cheater plugs on all my equipment or else I couldn't plug into the venue sound system(I wasn't touring with a large enough system for the venue at the time). This was by the supposed 'venue engineer'. Even after explaining, or trying to, what a ground loop was and the safe ways to address it they were insistent. I then proceeded to take the plugs, and conveniently 'forget' to plug in of my equipment in through the blasted things. Guess what, no ground loop. But the engineer was an idiot, and that combined with other reasons resulted in myself as TD and the stage manager calling the production company after the show and recommending they never go back to that venue again.

Even after the show went flawlessly with no hum or buzz the supposed 'engineer' still refused to listen to me when he noticed that his plugs were in a nice pile behind my sound board:)


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Raphbass



Joined: 30/12/06
Posts: 228
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1001430 - 02/08/12 05:08 PM
The average person identifies a symptom as a cause - "your mic is giving me electric shocks, there's something wrong with your mic."

Same as people will sometimes say "these speakers are making a funny noise". The answer is "well stop playing then". Sorry, a bit off-topic there!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dubbmann
active member


Joined: 17/03/04
Posts: 1404
Loc: 3rd stone from the sun.
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1001462 - 02/08/12 08:54 PM
hi hugh and seablade,

your responses make complete sense. the fidelity issue is certainly a factor and, above all, i agree w/t point made by s/b that a wireless workaround would only hide the problem. i have dealt with floating ground issues before, and know the sad stories of the gtrists of the pretenders and renaissance who died from these so i don't take the issue lightly. i was just wondering off the top of my head about a wireless solution/workaround. seems it would but that wouldn't protect the band or the crew, just the singer. and i don't sing, so that hardly matters ;-)

it would be great if SoS published a one page "how to" on using a volt-meter to check out a venue's power "rectitude" (DC power joke inserted here) but it might be academic to most bands due to the constraints of playing live ("ya wanna play or dontcha?"). i had a house that had a floating ground problem, probably due to a settling water-pipe that had been used to ground the circuit and the connection had broken, and it was a nightmare. i blew up some good gear there =:-O

d

--------------------
"Patsy had the drug tolerance of Keith Richards and the moral rectitude of Brian Jones." - Dr. Walter Bishop, "Fringe"


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dubbmann
active member


Joined: 17/03/04
Posts: 1404
Loc: 3rd stone from the sun.
Re: Well, yeah, again, electric shocks from mics !! new [Re: seablade]
      #1001463 - 02/08/12 08:58 PM
Quote seablade:



This is why I WILL yell at you(Be you a professional or one of my students) if I ever see you use a 'cheater' plug (3-Wire to 2-Wire). You CAN use them correctly, most people do not. To use them correctly REQUIRES running a third wire between the cheater plug ground and a safe building ground. Guess what, you shouldn't EVER remove an AC ground.

And to be fair, it isn't just pastors or guitarists that cause this. I have literally walked into a venue while I was touring and been told I had to use cheater plugs on all my equipment or else I couldn't plug into the venue sound system(I wasn't touring with a large enough system for the venue at the time). This was by the supposed 'venue engineer'. Even after explaining, or trying to, what a ground loop was and the safe ways to address it they were insistent. I then proceeded to take the plugs, and conveniently 'forget' to plug in of my equipment in through the blasted things. Guess what, no ground loop. But the engineer was an idiot, and that combined with other reasons resulted in myself as TD and the stage manager calling the production company after the show and recommending they never go back to that venue again.

Even after the show went flawlessly with no hum or buzz the supposed 'engineer' still refused to listen to me when he noticed that his plugs were in a nice pile behind my sound board:)




seablade,

+1. in my circles, "cheater plugs" are called "widow-makers" (a hat-tip to the late, great, oh-so-missed robert calvert on that one) for obvious reasons.

d

--------------------
"Patsy had the drug tolerance of Keith Richards and the moral rectitude of Brian Jones." - Dr. Walter Bishop, "Fringe"


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
CS70



Joined: 26/11/12
Posts: 94
Loc: Oslo, Norway
Re: Well, yeah, again, electric shocks from mics !! new [Re: Hugh Robjohns]
      #1041655 - 06/04/13 08:59 AM
Quote Hugh Robjohns:



If you're lucky it will just tingle unpleasantly. If you're unlucky there'll be a bang and the gig will come to a premature end... as will the person who formed the link in the circuit.





Best piece of advice ever. Just read your piece at http://www.performing-musician.com/pm/nov07/articles/techspe..., great stuff.

Thanks!

Edited by Hugh Robjohns (06/04/13 11:15 AM)


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
JonSSH



Joined: 19/07/10
Posts: 44
Loc: Yorkshire
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1043303 - 14/04/13 01:52 PM
static shocks are very unpleasant and can give you quite a fright. BBC TV centre is famous for them and doing "later with Jools' it could often be a problem. However they are a discharge.. they will dissipate and once you have had a shock you will not get one straight away again until you have built up a charge...
Repeating shocks are a voltage/fault problem.
I always meter between mic and guitar strings...
I also always try the mic with the back of my hand. If there is a large voltage present your hand will form a fist and instead of grabbing the mic it will be forced away potentially saving your life...

Please people learn about power and don't take risks... don't take off mains earth leads! Buy a meter! Look at yourt plugs every now and again... check that the leads are secure inside...

Buy a Martindale mains tester and leave it in a socket of your plug board always...


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
witzendoz



Joined: 09/04/13
Posts: 3
Loc: Fremantle Australia
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1045589 - 29/04/13 07:12 AM
Sorry if this has been mentioned, but I only zapped (excuse the pun) through the 5 pages.

One way you can get a shock between the mic and holding a guitar is if the PA system is plugged into one phase of a 3 phase supply and the guitar amp is plugged into a different phase of the 3 phase supply. This is because due to different loadings across the 3 phases there is sometimes a voltage differential. The volts you get hit with is unlikely to be the full 250 volts (thank goodness) but may be up to 50 volts which when hitting the lips feels like 1000 volts.

The PA and stage amps should be plugged into the same phase, then they should run the lighting rig from a different phase. This problem is hard to trace due to different nights / times of day, having a closer or wider voltage differential. The voltage differential also causes noise in the audio witch if often mistaken for a ground loop.

Alan.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1045984 - 30/04/13 07:59 PM
Sorry but that is complete bullshit in almost all ways, if you do not understand three phase power (and you clearly do not), please do not repeat myths about it.
They do nothing to enhance safety and are counter productive as they cause people to worry about unimportant things (which phase) as opposed to critical things (is all the metalwork bonded).

Three phase power is routine on stages bigger then the one down the local pub, and many amp racks of the bigger sort are built with three phase inputs, so tell me how is a rack full of amps wired to a three phase input supposed to be run off single phase?
I do normally try to keep all the backline on the same phase just because I have a power distribution chain for the back of the stage that is single phase, but if it ends up on two or even all three phases, it is not something I loose sleep over.

The one case where it can make a slight difference is where you have class II appliances on different phases as the touch current if getting between them can be slightly higher then normal, not generally a problem, and class II with no earth path is not that common on stage anyway.

99+% of the time complaints about hum due to lighting are really comments that the sound guy does not know how to design a rig with acceptable noise immunity or is doing something daft, do it right and your rig will not hum even if you are on the same phases as the lighting and in fact even if your dimmers are parked right next to the amp racks. Most non trivial lighting by the way is three phase input to the dimmer racks, as it is difficult to get much more then 125A as a single phase supply.

Seriously there are enough weird myths about power distribution in this game without adding to them, and safety mythology does nobody any favors.

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Hugh RobjohnsAdministrator
SOS Technical Editor


Joined: 25/07/03
Posts: 18369
Loc: Worcestershire
Re: Well, yeah, again, electric shocks from mics !! new [Re: dmills]
      #1046001 - 30/04/13 09:05 PM
Er... Yes! Well said Dan. Either Australia is a very scary place with a radically engineered three-phase system utterly at odds with the rest of the planet... Or our new friend is a tad confused!

H

--------------------
Technical Editor, Sound On Sound


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Bass Growler



Joined: 21/04/13
Posts: 11
Loc: Highlands of Scotland
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1046631 - 04/05/13 08:04 PM
What a fascinating thread! I'm a complete newbie as regards audio and completely out of my depth in this forum. As a newbie I'm taking the advice of all the folk who are replying to the threads for audio newbies - and I'm slowly learning about some of the basics.

Can I please appeal to all you audiophiles! Please pay the same respect to those who understand about AC power and its dangers and peculiarities when connected to sophisticated equipment.
Modern electrical kit has within its circuitry Safety Ground (Frame Ground) and many others. Logic Ground for electronic component circuits, Signal Ground for the Data path (Analogue or Digital) and I could go on. This is a complex subject. Many many electricians are connvinced that Ground is Earth and Earth is Ground so what does it matter - they all join up eventually!!! ------Wrong!!

Just as I will never know as much as recording engineers about recording - and as a result leave it to them for serious stuff - like recording our choir when it really matters, please hand over issues about electric shocks to folk who know their subject to a high level. I've been climbing up that learning curve for over 40 years and it includes attending more than one funeral, alas.

I don't want to get morbid - but please don't hand these issues over to the chap who knows how to wire a mains plug, and gets it right most of the time. This is serious stuff - and if I can lighten the issue - it has the potential to do significant damage to more than equipment. In the UK get a Martindale Tester to check all the outlets you use - if one fails - get help. Get all your kit PAT tested with a suitable tester - boring - yes - but the alternative is really shocking.









--------------------
I used to be indecisive, but now I'm not so sure!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
dmills



Joined: 25/08/06
Posts: 2129
Re: Well, yeah, again, electric shocks from mics !! new [Re: Bass Growler]
      #1046646 - 04/05/13 09:39 PM
Quote Bass Growler:


Modern electrical kit has within its circuitry Safety Ground (Frame Ground) and many others.




Which is usually the only one that matters from a safety perspective. All the others are merely functional not safety connections and so are not really a concern to the user (Particularly as they usually all come together inside the equipment anyway, "Technical earth" connections are not popular in live sound).
Quote:


Many many electricians are connvinced that Ground is Earth and Earth is Ground so what does it matter - they all join up eventually!!! ------Wrong!!




Not really from the point of view of an electrician as opposed to an electronics engineer, what matters is the frame ground, and as long as that has a low enough Ze to make the disconnect time and keep the touch voltage reasonable that is really all that matters.
Sure you get some old kit that separates the functional earth and frame ground connections to support the old 'clean earth' thing, but that does not really work in this age of mobile phones simply because the inductance is way too high.
Of course you also get kit that gets the screen connections horribly wrong, and hums like a bad singer, for which the answer is either a fat PEC or to telescope the audio cable screens (NEVER disconnect the frame ground).
Quote:


In the UK get a Martindale Tester to check all the outlets you use - if one fails - get help. Get all your kit PAT tested with a suitable tester - boring - yes - but the alternative is really shocking.




Also, get plug in RCDs and use them, they are a bit good at making most shocks merely painful rather then lethal.
I am a bit in two minds about the PAT thing for hobbyist musos mostly because IME a good visual inspection catches almost everything that the test box would, and that can and should be done every time the gear comes out, PAT is a bit like the MOT in that it only catches problems present when it is done, getting in the habit of inspecting for damaged cables and cord grips will catch most things as they happen.

I think however that for the most part we are in loud agreement!

My standard recommendation for papers by Walderon, Muncy, Whitlock and Ott goes here.....

Regards, Dan.

--------------------
Audiophiles use phono leads because they are unbalanced people!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
ef37a



Joined: 29/05/06
Posts: 5624
Loc: northampton uk
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1046663 - 05/05/13 06:07 AM
"Also, get plug in RCDs and use them"

You can also get RCDs that can be hardwired into dis'boards and socket strips and so cannot be forgotten.

Dave.


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Bass Growler



Joined: 21/04/13
Posts: 11
Loc: Highlands of Scotland
Re: Well, yeah, again, electric shocks from mics !! new [Re: ghc]
      #1046691 - 05/05/13 01:34 PM
Very happy with Dan and Dave's input. My comments regarding logic and Signal earths have been relevant in the past when equipment faults caused very unusual links between the differents earths.
To be fair, RCD has come to the aid of us all - before that, open circuit neutrals in particular have caused chaos, and the solution often tricky to sort out.
Cheers
Bass Growler

--------------------
I used to be indecisive, but now I'm not so sure!


Post Extras: Print Post   Remind Me!   Notify Moderator     Back to top
Pages: 1 | 2 | 3 | 4 | 5 | (show all)

Rate this thread

Jump to

Extra Information
0 registered and 30 anonymous users are browsing this forum.

Moderator:  David Etheridge, James Perrett, Paul White, zenguitar, Martin Walker, Forum Admin, Hugh Robjohns, Zukan, Frank Eleveld, Will Betts,  
Forum Permissions
      You cannot start new topics
      You cannot reply to topics
      HTML is disabled
      UBBCode is enabled
Rating:
Thread views: 202098

 

Home | Search | News | Current Issue | Tablet Mag | Articles | Forum | Subscribe | Shop | Readers Ads

Advertise | Information | Digital Editions | Privacy Policy | Support

May 2013
On sale now at main newsagents and bookstores (or buy direct from the
SOS Web Shop)
SOS current Print Magazine: click here for FULL Contents list
Click image for May 2013
DAW Tips from SOS
 

Email: Contact SOS

Telephone: +44 (0)1954 789888

Fax: +44 (0)1954 789895

Registered Office: Media House, Trafalgar Way, Bar Hill, Cambridge, CB23 8SQ, United Kingdom.

Sound On Sound Ltd is registered in England and Wales.

Company number: 3015516 VAT number: GB 638 5307 26

         

All contents copyright © SOS Publications Group and/or its licensors, 1985-2013. All rights reserved.
The contents of this article are subject to worldwide copyright protection and reproduction in whole or part, whether mechanical or electronic, is expressly forbidden without the prior written consent of the Publishers. Great care has been taken to ensure accuracy in the preparation of this article but neither Sound On Sound Limited nor the publishers can be held responsible for its contents. The views expressed are those of the contributors and not necessarily those of the publishers.

Web site designed & maintained by PB Associates | SOS | Relative Media