chris...
active member
Joined: 12/03/03
Posts: 4152
Loc: Glasgow
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: dmills]
#800166 - 02/01/10 07:13 PM
|
|
|
Quote dmills:
Indeed, anything
with a 13A socket on it (with very few specialist exceptions (of which an extension lead
is never one)), should have a earth connection.
Right!
Quote:
This is the sort of thing that begets two core cables for garden
use:
http://www.maplin.co.uk/Module.aspx?moduleno=13176
Note
that a two core cable with a 13A PLUG on one end and a female one of these on the other is
totally standard (and safe) as a cable for things like some flymo lawnmowers.
Yep - makes sense.
Quote:
What you should never
see is such a cable with a SOCKET on it.
Yep - understood.
Quote:
I would suspect someone
of modifying a lawnmower cable, but I suppose anything is possible.
As I said, he has no recollection of
modifying this extension - but I'll check again...
Thanks for your help!
Chris
|
adamb1026
Joined: 05/10/09
Posts: 60
Loc: Belfast, N.Ireland
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#803202 - 13/01/10 01:36 PM
|
|
|
Hey guys, been a while since I've been on here, thought I would keep you
updated. So far so good! No shocks in any venues...yet!  Bought the
Maplin plug tester and found one of my 4 way adapters had no earth!  . Bit red
faced when I saw only two lights Checked the guitarists plugs and the venues,
all of which so far are in good order. Here's hoping it continues  Thanks again guys for all of your help
|
plodsmeade
Joined: 03/01/06
Posts: 61
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Hugh Robjohns]
#834561 - 19/05/10 05:19 PM
|
|
|
Quote Hugh Robjohns:
If one
or other of those mains safety earths becomes high resistance or disconnected, then the
mains input filtering of the amp or mixer will tend to pull everything connected to the
now disconnected earth line up to half mains volts (115V in the UK and Europe).
I'm not sure I fully understand
how the 115V float works, in so far as what's going on in the device?
Is it
something like the voltage is +/- 115V relative to ground only (giving the device the 230V
range in use)?
|
Sheriton
Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: plodsmeade]
#834572 - 19/05/10 06:03 PM
|
|
|
|
It's usually capacitors connected between the live and neutral and the earth. Without an
earth reference, it'll float up to a point halfway between the L and N terminals i.e.
115v.
You can see the same phenomenon on class II equipment like DVD players
that employ similar filtering. If you measure the potential of the case with respect to a
good earth, it'll be in the region of 115v. It's quite safe to touch as there's no
significant amount of current available to do you any damage. If you connect a lot of
class II equipment together though, you can sometimes feel a bit of a tingle...
-------------------- There's nothing we can't face... Except for bunnies
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: plodsmeade]
#834602 - 19/05/10 08:39 PM
|
|
|
Quote plodsmeade:
Is it something
like the voltage is +/- 115V relative to ground only (giving the device the 230V range in
use)?
No. That arrangement
would be 'balanced mains' which brings with it a whole host of other issues -- both good
and bad.
In general, single phase mains supplies operated as an unbalanced
system. The neutral is tied to the earth (ground) and the live carries (in Europe) 130V AC
relative to that.
To help get rid of any nasty high frequency rubbish on the
supply lines, it is common practice, as Sheriton says, to employ bypass capacitors between
the live-earth and neutral-earth. That way, any high frequency rubbish gets passed
straight into the earth line and away from the equipment.
However, if the
equipment safety earth is missing because of a miswired plug or other fault, or if it is a
class II (double isulated) device, then what would have been the earthed point of the
capacitor interconnection gets dragged up to half the total voltage across both capacitors
-- 115V in Europe.
Again, as Sheriton says, the size of the capacitors and the
impedance of the supply lines means that no appreciable current is likely to flow..... but
if you have several devices all sitting across the mains, each passing some current, then
there can be sufficient to give a nasty tingle if not a lethal belt.
With
normal mains-earthed equipment, shocks from the metal work are an obvious and definite
indication of a serious fault. With Class II devices, it shouldn't happen, but it can and
it doesn't necesarily indicate a fault... but is certainly annoying.
Thankfully, it is easily fixed by providng a proper safety earth and a lot of equipment
is designed with this option in mind.
Hugh
-------------------- Technical Editor, Sound On Sound
|
plodsmeade
Joined: 03/01/06
Posts: 61
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#834798 - 20/05/10 03:49 PM
|
|
|
|
thank you both, that seems to make sense.
so the 115V is relative to earth, so
touching anything earthed is likely to cause a shock, such as a radiator or earthed casing
on another unit, not just the mic-mixer-earth?
|
Nathan
Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: plodsmeade]
#834883 - 20/05/10 09:24 PM
|
|
|
Quote plodsmeade:
...so the 115V is relative to earth, so touching anything earthed is likely to cause a
shock, such as a radiator or earthed casing on another unit, not just the mic-mixer-earth?
No, as the earth conductor
is not connected to the supply-earth, only things connected to your equipment or metal
casing, guitar bridge, strings, etc will rise to this voltage.
Real problem is
if there is a serious live to casing fauly on your gear while the earth conductor is
compromised -then it's not uncomfortable, it's lethal!
>
-------------------- planet nine
lincoln, uk.
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: plodsmeade]
#834927 - 21/05/10 08:15 AM
|
|
|
Quote plodsmeade:
so the 115V is
relative to earth
Yes. I
think Nathan may have misunerstood what you meant.
Quote:
so touching anything earthed is likely to cause a
shock, such as a radiator or earthed casing on another unit, not just the mic-mixer-earth?
Yes. Because your body
then forms a circuit between the case which is floating at 115V, real earth, the earthed
neutral at the substation and back to the box.
Hugh
-------------------- Technical Editor, Sound On Sound
|
Nathan
Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Hugh Robjohns]
#835224 - 23/05/10 10:10 AM
|
|
|
|
Yes, I agree Hugh, I think I got the wrong end of the stick there...
>
-------------------- planet nine
lincoln, uk.
|
Lalala Music
Joined: 26/07/10
Posts: 22
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#848774 - 26/07/10 08:42 AM
|
|
|
Ahh the electric shock issue! Have had that a couple of times before. I'm a guitarist and
singer for Her Sweet Suicide, and had these shocks a while back. My rig mainly consists of
an unearthed POD Live... so you can already figure out where the shocks are coming from. I
am merely conducting some form of electricity to the mic by touching the guitar, and well,
I'm then getting shocked on my lips. That's one hell of a kiss of death! Solution: Bought an extension cord which had a third earth prong! All good now! Cheers, Patrick
-------------------- Hi my name is Patrick. I run Lalala Music an online music business plan to help musicians create, promote, distribute and perform their music.
|
Nathan
Joined: 13/09/04
Posts: 1872
Loc: lincolnshire government experi...
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Lalala Music]
#849270 - 27/07/10 07:24 AM
|
|
|
|
I take it that you Pod Live is not double insulated, ie it needs its earth connection.
>
-------------------- planet nine
lincoln, uk.
|
damoore
Joined: 05/07/09
Posts: 326
Loc: New Hampshire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Statick]
#856025 - 24/08/10 01:03 AM
|
|
|
Quote Statick:
so the
moral is, i guess, test all the extensions as well, especially if it's venue-owned gear
and not your own.
Saw this
once in an amusing way. Well, it seems amusing now. Was working late and the cleaners were
vacuuming. A cleaner got in the lift and went upstairs but only half her extension cord
went with her. She got half a flight up and the cord caught on the doors and the lift came
to a shuddering halt. We couldn't get it to go down again so I got the office tool kit and
removed the plug so the cord would slide through the doors and the lift would continue to
the next floor.
After we retrieved the cleaner and the cord I looked at it
intending to reconnect it and thought to check the far end. Turned out the other end was
miswired! No idea if the end I had taken apart had been miswired the same way. At that
point I refused to put it back together. I was kind of spooked - if I had just gone ahead
and connected it up "properly" I would have unwittingly produced a cross-wired extension
cable.
Moral is it does matter that the cable is correctly connected at both
ends. Just having three random wires make the correct connections is not good enough. That
and don't assume the previous guy did it right.
|
martin randle
member
Joined: 03/03/00
Posts: 246
Loc: cambridge uk
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#950359 - 30/10/11 09:19 PM
|
|
|
This same thing happened to me last night (shock off the mic) all the gear we were using
(PA mixer guitar amps keyboards were running off one double socket via extension leads. I
only use the same leads and have never experienced this before - however we have never
played at this venue before. my girlfriend came up with a classically simple
idea and went to my car and came back 2 minutes later with my rubber floor mats. I stood
on these all night and didn't get another shock. I will get a circuit tester
before I play there again. (The Social Club Witchford Ely Cambs UK)
-------------------- http://www.myspace.com/cottonsalamander
|
TSH-Tim
Joined: 21/02/11
Posts: 816
Loc: Guildford
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#950363 - 30/10/11 09:37 PM
|
|
|
Buy yourself a plug tester (£3.50 from CPC)
-------------------- PA Hire Surrey
Lighting Hire Surrey
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: TSH-Tim]
#950446 - 31/10/11 01:20 PM
|
|
|
|
Yes -- I would stringly advise NEVER plugging anything into a wall socket until you've
tested it with a simple mains-tester plug. I've come across way too any pubs, clubs and
conference venues with missing earths and L-N reversals.
Also, once you've
tested the socket and you know it is safe, ALWAYS plug the equipment in via RCDs, just to
make absolutely sure!
hugh
-------------------- Technical Editor, Sound On Sound
|
Gary_W
Joined: 18/10/06
Posts: 376
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993390 - 18/06/12 01:34 PM
|
|
|
I'd like to thank everyone for the info in this thread - I need to find the culprit of a
tingle here. I've played live twice over the last 3 weeks. At both venues,
I've had shocks to the lips. I play guitar and sing, though in this band I'm not singing
often.... Just as well. It was a mild tingle at venue #1 and sparks, noise and pain at
venue #2..... It was too much to be DC - the culprit felt like a reasonably high
potential difference between my guitar bridge and the microphone. Interesting to read
here about the float up to 115v as this seems to make sense. This was not 'tongue on a 9v
battery' - rather more impressive unless I'm being a complete fairy.... Fortunately our
bass player had one of the mic pop shields of the hair bear bunch variety which provided
ample insulation (no, I am not suggesting this as a solution to my problem before anyone
gets excited but this obviously stopped the issue of sparky lips  ) I will double check it tonight, but I actually tested the earth bonding on my amp a few
weeks back (I had a friend test it to medical grade standards which tested earth bonding,
mains leakage, the works and it's spot on and as an owner of a multimeter I'm no stranger
to keeping myself alive!). I may have swapped mains leads but all of my mains leads are
in good condition so I'll be surprised if it's that. But multimeter from earth to my
guitar bridge will be the first thing I do just to rule out that bit. One
question here - folks are mentioning double insulated equipment potentially having a
potential...... On my pedalboard, I have several pedals run from a 9v power supply - I
can't see how it can be them (if my guitar earth is indeed good as suspected then 9v to
earth is just going to drag the 1700mA supply down isn't it?). I also have a couple of
Carl Martin pedals (a Quattro and a chorus). These have 2 core mains going to them and
are both double insulated. So could it be one of them? Can anyone tell me a
bit more about this double insulated upping the earth potential thing or have I
misunderstood? Obviously I'll test tonight with just amp and guitar and then add the
pedalboard back in. I'm hoping for no issues at my end which leads me to external
problems (venue / pa / extension leads). On the two occasions it happened it
was 2 different venues and 2 different PA's. One thing that was common was a few
extension leads (provided by another band member). So, unless we have 2 dodgy PA's and 2
dodgy venues then the extensions are likely culprits are they not? Thanks Gary
|
Gary_W
Joined: 18/10/06
Posts: 376
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993466 - 18/06/12 07:23 PM
|
|
|
OK, I've tested my gear out and all appears fine.... I have a good earth to my amplifier
and this continues on to the bridge of my guitar. With the pedal board in, it adds about
2 ohms of resistance (according to my meter whose tollerence is not great). In
short, I have under 3 ohms between my guitar bridge and the house wiring according to the
aforementioned cheapo meter. So it's OK in my opinion but correct me if you disagree  I also tested for AC and DC voltage. Unsurprisingly with a decent earth, there was
none. So if I am properly earthed on the guitar side of things, the
posibilities are:- 1. Broken earth in the extension lead supplying my guitar
kit 2. Broken earth at two different venues (possible but less likely) 3. Broken
earth on two seperate mixers (again less likely) So favourite culprit is option
1 in my opinion - any advance on that? Many thanks Gary
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Gary_W]
#993482 - 18/06/12 08:59 PM
|
|
|
|
My vote is for a dodgy mains extension. Best advice if you want to live is (a) never use
someone's else's mains extensions and (b) ALWAYS test every wall socket and mains
extension socket with a pukka mains tester before you use them!
It's
disturbingly common to find wall sockets with dodgy earths, so please do check. But given
the common factor of a mains extension I think you would be well advised to get that
checked pronto!
Regarding the double-insulated pedals, they are grounded
through the guitar amp, which you have proven is properly grounded when plugged into a
decent grounded mains outlet.
To sum up, my advice would be (1) to buy a
simple plug-in mains socket tester and use it on every wall socket and mains extension
every time you rig your gear; (2) invest in a plug-in RCD unit for your gear--it will save
your life should the worst happen with a dodgy earth somewhere; (3) get those mains
extensions tested and repaired as a matte of urgency.
Hugh
-------------------- Technical Editor, Sound On Sound
|
Gary_W
Joined: 18/10/06
Posts: 376
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993511 - 19/06/12 07:40 AM
|
|
|
|
Thanks Hugh - I really appreciate the advice. I will invest in a socket tester and ensure
I take my own extension lead.
It's clear that my guitar earth is at earth
potential (where it should be) and that my zapping here came from something else - at the
first gig, I was straight into a socket but this time I was using an extension.
Whilst I can avoid my guitar ground floating up by socket tester + own good extension
lead, I can still get in trouble if the mixer has a floaty ground can't I? So we're
talking about the scenario where it really is the mic giving the shock, not the mic being
the decent earth (as seems to mostly be the case here). So unless I become 'band
electrician' I'm still stuffed BECAUSE I've got a good earth on my own kit.....
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Gary_W]
#993524 - 19/06/12 09:05 AM
|
|
|
Quote Gary_W:
Whilst I can avoid
my guitar ground floating up by socket tester + own good extension lead, I can still get
in trouble if the mixer has a floaty ground can't I? So we're talking about the scenario
where it really is the mic giving the shock, not the mic being the decent earth (as seems
to mostly be the case here). So unless I become 'band electrician' I'm still stuffed
BECAUSE I've got a good earth on my own kit.....
Yes, there are two ways of getting electocuted in this kind of
situation!
The first is where the mic is properly earthed bu the guitar goes
live, and the second is wher the mic goes live but the guitar is earthed. In both cases
your body closes the circuit.
The good news is that unless there is a really
serious fault somewhere, the mic is unlikely to reach full mains voltage. Worst case is
that it might 'float' up to half-mains voltage (115V in the UK) if the PA equipment is
ungrounded, and that would be from a relatively high impednace, so while unpleasant it's
unlikely to be lethal. But it is an extremely unlikely situation in the first place since
all power amps are class 1 devices (afaik) and they would impose a solid safety ground on
the PA system anyway.
The only totally safe solution that protects you
regardless of where the earth goes missing, is to always power your equipment via a good
quality RCD. That way, if some of the mains current from either system ends up going
somewhere it shouldn't via you, it will trup the power before it can do any serious
damage.
Hugh
-------------------- Technical Editor, Sound On Sound
|
Gary_W
Joined: 18/10/06
Posts: 376
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993552 - 19/06/12 12:20 PM
|
|
|
Thanks again, Hugh  With regard to RCD's, it's all very well protecting my equipment
(and I'll ensure I do so) but this still won't protect me from a dodgy mixer (for example)
that has been brought and set up by someone else will it? As my guitar is well grounded,
if my RCD detects current to earth it'll trip out MY RCD. As the offending live part is
the microphone here which is coming from a mixer I'm not better off as that will keep
going and passing me the juice!! It's one of those situations where it's a very
necessary conversation for a guitar player / bassist as you have both hands on a perfect
earth connection. As such, you are at the mercy of other folks equipment / venue wiring
more than most band members. You are in the position of being worse off if your kit IS
perfectly grounded if someone else's is not! I think I need a chat....
|
Sheriton
Joined: 27/01/03
Posts: 1554
Loc: Leicester, UK
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Gary_W]
#993558 - 19/06/12 01:07 PM
|
|
|
Quote Gary_W:
As my guitar is
well grounded, if my RCD detects current to earth it'll trip out MY RCD.
Note quite. Your RCD will only trip if it
detects an imbalance between the live and neutral currents flowing through your own kit;
it doesn't measure current flowing through the earth connection. So it won't trip if
you're getting zapped by someone else's faulty kit. On the plus side, that does give you
an indication of where the stray current is coming from - if your RCD hasn't tripped, it's
probably not coming from your mains supply.
-------------------- There's nothing we can't face... Except for bunnies
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Gary_W]
#993579 - 19/06/12 02:36 PM
|
|
|
|
You're right -- if the PA system is live and grounding via your system your RCD won't help
because it won't interrupt the ground -- but it might still trip if it senses an imbalance
of current on the supply.
If you have any doubts about the PA system, look for
the PAT stickers -- ask to see the PAT records. Check if they are running their gear
through RCDs... and if in doubt, be careful not to touch anything metallic!
And
if you do detect anything that you're not happy about, make sure you get those responsible
for the kit to investigate properly.
hugh
-------------------- Technical Editor, Sound On Sound
|
Gary_W
Joined: 18/10/06
Posts: 376
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993659 - 20/06/12 06:33 AM
|
|
|
Thank you both - eBay socket tester is in the post and I will be multimetering the rest of
the bands extension leads. Also going to take my DMV to the next venue so as, if anything
daft DOES happen I can get a bit more buy-in from everyone..... If it says there is
voltage it then makes it a lot more believable vs folks thinking I'm wearing nylon
|
Jorge
member
Joined: 13/12/03
Posts: 324
Loc: New York, NY
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993663 - 20/06/12 07:45 AM
|
|
|
I don't know how common this is, either in the US or UK, but the subject of Reverse
Polarity Bootleg Ground wiring in venues has been discussed on another forum. RPBG is one
possible explanation for electric shocks from mics, and could potentially lead to fatal
shocks.
I know nothing about electrical wiring in the UK, but for US 120 v
three conductor circuits, a Bootleg Ground is when, if no true ground is available, the
outlet neutral is connected to the outlet ground. This in itself is not usually a problem.
Occasionally, however, on top of the Bootleg Ground miswiring, the building neutral is
mistakenly switched with the building hot (Reverse Polarity). When what is thought to be
the building hot and neutral leads are then connected to the outlet hot and neutral leads,
respectively, what actually occurs is that the building hot is connected to the outlet
neutral and the outlet ground (RPBG). This, unlike simple Reverse Polarity, or a simple
Bootleg Ground, can cause the case and ground of devices (eg, mixer chassis, mic, guitar
strings) to be at live potential. Not a problem until a person touches both that and an
actual ground. Then (and this would happen commonly) the person will get a shock,
potentially at high voltage.
The problem is that your simple outlet ground tester
will find most faults but completely misses the RPBG configuration. You need in addition a
noncontact tester that will identify a hot wire without actual metal to metal contact or
access to a true ground. Here is a video that explains a simple procedure to find RPBG
wiring. A noncontact tester could also find a high voltage (>90 volts) hot chassis,
guitar strings, mic cable or mic.
http://www.youtube.com/watch?v=iLk-6pvSlWg&feature=plcp
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Jorge]
#993675 - 20/06/12 08:39 AM
|
|
|
Quote Jorge:
I don't know how
common this is, either in the US or UK, but the subject of Reverse Polarity Bootleg Ground
wiring in venues has been discussed on another forum.
It's a very scary bodge, but thankfully not likely to happen in
the UK. I have heard of similar situations in other countries though!
The
reason it is so prevalent in the US is because a lot of buildings are fed with what is, in
effect, a balanced 230V mains feed with a centre neutral. Some sockets are then run from
one side and centre neutral (giving the 115V supply), while other sockets are run from the
other side and neutral. Devices that require a lot of power -- like washing machines and
so on -- are often powered from the 240V supply directly.
The centre neutral is
normally bonded to earth at some point to make the 115V supplies 'unbalanced' in the
conventional way, and hence some electricians have been known to indulge in the lazy
practice of using the neutral as a makeshift earth rather than run a proper earth cable to
the mains sockets.
However, if things then get confused elsewhere in the
building it is possible for the live and neutral wiring to end up being reversed,
potentially resulting in equipment cases becoming live relative to a genuine earth (like
the water pipes and CH radiators!).
In the UK, because we only have a 240V
supply in domestic buildings, and because the IEE wiring regulations are so strict, we
can't suffer the RPBG syndrome you describe for the US. It could potentially happen in
buildings with 3-phase supplies, but again, the wiring regulations are so strict that it
just won't happen.
Quote:
The problem is that your simple outlet ground tester will find most faults but
completely misses the RPBG configuration. You need in addition a noncontact tester that
will identify a hot wire without actual metal to metal contact or access to a true
ground.
Yes... it would be a
bit of a worry! For all it's faults, there are many good things about living in the UK!

hugh
-------------------- Technical Editor, Sound On Sound
|
Dave Gate
active member
Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993702 - 20/06/12 09:32 AM
|
|
|
|
Many years ago, before the UK switched to the European standard for three phase colour
coding (green for Earth, blue for neutral and brown/black/grey for the three lives) I was
working on a show in what had been a reasonably famous venue (no names) where the three
phase mains had to be tailed in by an electrician. Who attached the blue live phase cable
to the neutral, and the black neutral cable to the live phase that should have had the
blue cable.
Oh that was fun when the power went on
-------------------- Gear List: reverse only.
|
Jorge
member
Joined: 13/12/03
Posts: 324
Loc: New York, NY
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993754 - 20/06/12 02:17 PM
|
|
|
|
Thank you Hugh for that crystal clear explanation. Yes there are some downsides to the
anti-regulatory ideology and/or poor enforcement of regulations that have become so
prevalent in the US. The good news is no one I know has ever been electrocuted by an RPBG
wiring configuration or anything else. Just to be safe, however, I have just ordered a
noncontact tester and will add that to my wall outlet testing routine in the venues we
play.
|
seablade
Joined: 21/11/04
Posts: 3768
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Dave Gate]
#993757 - 20/06/12 02:19 PM
|
|
|
Quote Dave Gate:
Many years ago,
before the UK switched to the European standard for three phase colour coding (green for
Earth, blue for neutral and brown/black/grey for the three lives) I was working on a show
in what had been a reasonably famous venue (no names) where the three phase mains had to
be tailed in by an electrician. Who attached the blue live phase cable to the neutral,
and the black neutral cable to the live phase that should have had the blue cable.
Oh that was fun when the power went on
Remind me never to touch UK/EU power. In the US the standard is
Green = Ground, White = Neutral, and Red, Blue, Black for the three phases. Would be way
to confusing.
I can't think of any place I have ever run across with hot
swapped to ground and neutral on the hot for the record, scary thoughts there that that
can even exist.
Hugh is correct on the basic wiring for most houses in the US
(Commercial buildings tend to have true 3-phase though). But even in houses a fairly
standard coloring is used, where there is not usually differentiation between phases, but
rather the hot is usually black with neutral white and green ground. For 220v in the US
Red and Black are usually hot and White is still Neutral with Green for Ground.
Seablade
|
Dave Gate
active member
Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993761 - 20/06/12 03:24 PM
|
|
|
|
It used to be very confusing here, which is where the offending electrician went wrong.
Three phase mains had Earth = green, Neutral = black, Red/Blue/Yellow = 3 x live; but
single phase had Earth = green & yellow, Neutral = blue, Live = brown.
This
is one area where we can wholeheartedly thank the EU for imposing a standardisation . . .
-------------------- Gear List: reverse only.
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Dave Gate]
#993859 - 21/06/12 09:21 AM
|
|
|
Three phase power isn't something I get to play with these days, but when I did it was
red, blue, and yellow and I think if I was presented with brown, black, gey cables today
I'd be scratching my head with them!
The definition of a competent person is
someone who knows when they don't know enough, and stands back to let someone better
trained take over!
hugh
-------------------- Technical Editor, Sound On Sound
|
Dave Gate
active member
Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#993871 - 21/06/12 09:47 AM
|
|
|
|
I was there at the changeover, and had to get my venue's old Red/Blue/Yellow Camlock
outlets and cables converted to Brown/Black/Grey Powerloks. But the new colours make more
sense, as the earth, neutral and first live phase are in line with what you'd find in a
single phase UK mains plug.
-------------------- Gear List: reverse only.
|
Hugh Robjohns
SOS Technical Editor
Joined: 25/07/03
Posts: 18387
Loc: Worcestershire
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Dave Gate]
#993906 - 21/06/12 11:08 AM
|
|
|
|
I agree it makes sense in the wider construct -- but red, blue and yellow, all being
bright colours, shouted 'live' to me. Brown black and grey are all pretty earthly
colours....
hugh
-------------------- Technical Editor, Sound On Sound
|
Dave Gate
active member
Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Hugh Robjohns]
#993908 - 21/06/12 11:13 AM
|
|
|
|
That sounds like the old UK wiring system (before my time!) where red was live and black
was neutral (can't remember what earth was). You still find that in domestic wiring
behind the sockets and switches, with the earth usually being an unshielded core (which
most sensible people slip a green and yellow sheath over!). If you've ever changed a
socket or a lightswitch you'll know what I mean.
-------------------- Gear List: reverse only.
|
Raphbass
Joined: 30/12/06
Posts: 228
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#997166 - 11/07/12 10:58 AM
|
|
|
|
On a gig last Saturday, the guitarist plugged into a different socket to the rest of us -
there was what felt like a good 100+ voltsAC between his strings and his mic that was
going into the PA. When he first mentioned it I thought he meant the common little static
"zap" you sometimes get - I didn't realize till I myself touched his strings and the mic
at the same time that it was a serious buzz - I remember from messing about with
transformers as a kid what 120V AC feels like, this was similar.
I got him to
plug into a plugboard on the same wall socket as the rest of us and the problem was
solved. Not sure whether I should have informed the venue that there was an issue between
two earths in different sockets in the same room - or is this normal?
I assume
that for example if they plug in two brass standard lamps or similar, one on each wall
socket, that the guy holding both would be getting a good dose of current and if the two
lamps came into contact there would be a shower of sparks between them.
I've
always assumed that earth is earth is earth - I don't quite get how two earths can be so
many volts apart, unless something's gone terribly wrong with the building's wiring. This
is a posh modern hotel by the way, not a crumbling third-world establishment (and I've
seen a few!).
|
Raphbass
Joined: 30/12/06
Posts: 228
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#997170 - 11/07/12 11:08 AM
|
|
|
|
PS - re colours - yes, brown seems to me the most earthly of all colours, how that got to
be "live" totally beats me. And given that a common symptom of colour blindness is to
confuse green and brown it seems mental to have the two close together in a mains plug.
What was wrong with red for live?
|
seablade
Joined: 21/11/04
Posts: 3768
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Raphbass]
#997177 - 11/07/12 11:18 AM
|
|
|
Quote Raphbass:
On a gig last
Saturday, the guitarist plugged into a different socket to the rest of us - there was what
felt like a good 100+ voltsAC between his strings and his mic that was going into the PA.
When he first mentioned it I thought he meant the common little static "zap" you sometimes
get - I didn't realize till I myself touched his strings and the mic at the same time that
it was a serious buzz - I remember from messing about with transformers as a kid what 120V
AC feels like, this was similar.
If it was a true shock from incorrect grounding that indicates two things. First
that the socket ground was a much higher impedance than it should be(Bad connection) or
missing(No connection). And that there was likely a fault inside of the guitar amp that
needs to be checked out.
Quote:
I got him to plug into a plugboard on the same wall socket
as the rest of us and the problem was solved. Not sure whether I should have informed the
venue that there was an issue between two earths in different sockets in the same room -
or is this normal?
Yes
they need to be informed.
Quote:
I assume that for example if they plug in two brass
standard lamps or similar, one on each wall socket, that the guy holding both would be
getting a good dose of current and if the two lamps came into contact there would be a
shower of sparks between them.
Not unless there was some VERY bad wiring in the venue, or there is a fault in the
lamp attached to the socket with the bad ground.
Seablade
|
Dave Gate
active member
Joined: 02/02/04
Posts: 1353
Loc: M6/M61/M60/M62/M65
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: Raphbass]
#997195 - 11/07/12 12:08 PM
|
|
|
Quote Raphbass:
PS - re colours -
yes, brown seems to me the most earthly of all colours, how that got to be "live" totally
beats me. And given that a common symptom of colour blindness is to confuse green and
brown it seems mental to have the two close together in a mains plug. What was wrong with
red for live?
For domestic
use it's supposed to be green and yellow striped. So, for colour-blind people you have a
dark colour, a light colour and stripes. Not sure how effective it is, though.
-------------------- Gear List: reverse only.
|
dmills
Joined: 25/08/06
Posts: 2130
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: ghc]
#997316 - 11/07/12 10:30 PM
|
|
|
|
Red/Green/Black was replaced for flexible cables many years ago precisely because of the
problem of red/green colour blindness (Back when appliances commonly came without plugs),
a red/green reverse in the plug would leave the case live, and this was in the days before
RCDs!
This left us with the interestingly odd situation in that single phase
flexible cables were brown/blue/green-yellow, three phase flexible cables were usually
brown/black/grey with a blue neutral and the usual striped earth (EU standard). Fixed installation wiring however was usually red/black/green-yellow for single phase or
red/blue/green-yellow/black(neutral) for three phase (Note that blue means different
things depending on whether the wiring is a flex(Neutral) or installation(Phase)). Note
also that a single phase circuit fed from any phase was usually red/black.....
Anyway all this got harmonised across Europe with the new scheme being brown/blue for
single phase circuits, black/brown/grey + blue neutral for three phase, this is the same
for both fixed install wiring and flexible circuits. It caused some few problems (and a
very few expensive mistakes) when first introduced, but the fact that in a modern install
blue has only one possible meaning (neutral) is on aggregate a net win.
The
only striped wire in common use for mains voltage is the green/yellow one that is only
ever used for earth connections and is two colours precisely so that no matter what colour
vision problems you have it is obvious.
That concludes a short history of UK
wiring.
Regards, Dan.
-------------------- Audiophiles use phono leads because they are unbalanced people!
|
Raphbass
Joined: 30/12/06
Posts: 228
|
Re: Well, yeah, again, electric shocks from mics !!
[Re: seablade]
#998192 - 16/07/12 05:28 PM
|
|
|
Quote seablade:
Quote Raphbass:
On a gig last
Saturday, the guitarist plugged into a different socket to the rest of us - there was what
felt like a good 100+ voltsAC between his strings and his mic that was going into the PA.
When he first mentioned it I thought he meant the common little static "zap" you sometimes
get - I didn't realize till I myself touched his strings and the mic at the same time that
it was a serious buzz - I remember from messing about with transformers as a kid what 120V
AC feels like, this was similar.
If it was a true shock from incorrect grounding that indicates two things. First
that the socket ground was a much higher impedance than it should be(Bad connection) or
missing(No connection). And that there was likely a fault inside of the guitar amp that
needs to be checked out.
Quote:
I got him to plug into a plugboard on the same wall socket
as the rest of us and the problem was solved. Not sure whether I should have informed the
venue that there was an issue between two earths in different sockets in the same room -
or is this normal?
Yes they need to be informed.
Quote:
I assume that for example if they plug in two brass
standard lamps or similar, one on each wall socket, that the guy holding both would be
getting a good dose of current and if the two lamps came into contact there would be a
shower of sparks between them.
Not unless there was some VERY bad wiring in the venue, or
there is a fault in the lamp attached to the socket with the bad ground.
Seablade
Well yes there
was a comedy moment as I looked at his 20yr-old Fender amp and he sort of took umbrage and
said with a dry hint of confrontation "never had a problem before", and he then looked
just as implicatingly (if that's a word!) at my mixer which is less than a year old, and
PAT tested fairly recently... and there we stood for a few seconds in a stalemate. [Cue
soundtrack to "the Good the Bad and the Ugly"]
In retrospect, I feel pretty
pathetic that it didn't occur to me to get out the mains tester I have in my kit.
If there's a fault in the mains of one of the circuits, couldn't it render the
earth live even without a fault in the gear? Haven't thought it through (and unlikely to
bother!) but it seems it can't be a simple reversal of live and neutral as the amp was
working fine, and the rogue voltage was a lot less than mains (about half I reckon).
Anyway I've emailed the venue to suggest they should check what's going on in
their mains sockets.
|