PAT testing - Is it legally required
Postby The Fold Studios » Wed Apr 20, 2011 10:55 am
Question is in the title really. I am self-empployed and run a small recording studio. Am I in trouble if I don't have PAT testing on all my appliances?
The Fold Studios
Re: PAT testing - Is it legally required
Postby chris... » Wed Apr 20, 2011 11:17 am
chris...
Postby Howdy Doody Time » Wed Apr 20, 2011 3:23 pm
Excellent question, - Brilliant answer 8-)
Howdy Doody Time
The only excuse we have for making music in the first place is to make it differently..vis-a-vis our own difference (Glenn Gould)
Postby chris... » Wed Apr 20, 2011 5:56 pm
Some insurance companies may mandate it. But that's a different question from "is it legally required".
chris...
Postby dmills » Thu Apr 21, 2011 12:46 am
The requirement under the electricity at work act (or is it PUWER, I can never remember) is that reasonable measures are taken to ensure that equipment used at work is electrically safe.
Now often the easiest way to do that is to PAT it once in a while (It does NOT automatically have to be annual, should be determined by risk assessment), but you are free to come up with an alternative approach.
I tend to view the PAT week as a good opportunity to check all the screws are tight, clean things check connectors for damage, all that boring stuff that otherwise never gets done.
If you do it right you will find 99+% of the problems before the gear goes anywhere near the test box, a good visual inspection will reveal the vast majority of problems.
Incidentally it is very much worth doing earth bond checks on NEW gear and checks for correct connection on new IEC leads, I have had both fail in scary ways.
Regards, Dan.
dmills
Postby The Bunk » Thu Apr 21, 2011 9:07 am
With these kinds of issues it's very much about your approach to good housekeeping and, dare I say it, health and safety. Legally there's no recourse against you if you haven't PAT tested but if something happens - let's just say an electrical fire - at the studio, you could end up with all sorts of people coming in to inspect / investigate the cause of the fire etc. If they discover you haven't been PAT testing, that'll tell them you've got a slightly slack approach to H+S and they might crawl all over you. If you demonstrate that you do take these kinds of issues seriously it'll put you in a much better position.
The Bunk
Postby planetnine » Fri Apr 22, 2011 12:04 am
The Bunk wrote:With these kinds of issues it's very much about your approach to good housekeeping and, dare I say it, health and safety. Legally there's no recourse against you if you haven't PAT tested but if something happens - let's just say an electrical fire - at the studio, you could end up with all sorts of people coming in to inspect / investigate the cause of the fire etc. If they discover you haven't been PAT testing, that'll tell them you've got a slightly slack approach to H+S and they might crawl all over you. If you demonstrate that you do take these kinds of issues seriously it'll put you in a much better position.
"PAT Test" tends to mean a test compliant to the IEE Guide to in-Service Test & Inspection, complete with requirement for little green stickers. It is not enforceable unless referred to specifically in a contract. PAT test could mean other testing and inspection methods.
Dan answered fairly here, that is not a legal requirement, but if you engage in any business activity which uses any mains-powered electrical equipment, you should really have some kind of checking and maintenance policy to comply with health and safety, and it would be sensible to write down the results of any said check or fixes. You're most of the way to complying with the guide by this point though ;)
HSE have repeatedly railled against the electrical contractors' industries encouragement of the "Need a sticker to be legal" assumption, insisting that it is over officious for (eg) many office and shop situations.
But as Dan says, it is an opportunity to find gremlins in your gear. I gave up fighting it all and bought a computerised tester -the database helps me keep track of tests and equipment locations, and as electrical testing is easy and almost automatic, I actually test many larger flex cables very regularly -some before each job for peace of mind.
It's not just a safety issue, but one of reliability also, and I really don't want my mains cables to let me down mid-event.
I tend also to use my PAT stickers just for identification (asset number), and my database for the pass and date info. That upsets council inspectors, but it is entirely legal and proper (I would bring test results lists/certs here).
Remember, the IEE Guide's methods are just one way of checking your electrical gear, and are not law in themselves. That said, they are good practice.
planetnine
Planet Nine, Lincoln, UK.
Postby dmills » Fri Apr 22, 2011 1:35 am
Nathan wrote:
I gave up fighting it all and bought a computerised tester -the database helps me keep track of tests and equipment locations, and as electrical testing is easy and almost automatic, I actually test many larger flex cables very regularly - some before each job for peace of mind.
Which to my mind sort of misses the point, it is NOT the test box that should be finding problems, it is the visual inspection!
The test box will for the most part only find things that are already broken, where a good visual (inspect the whole cable for nicks and other damage, open up the plugs and make sure the screws are tight and the fuse is appropriate), will often find loose screws, heat discolouration, damaged fuse holders....
I have I think twice out of several thousand tests had the box tell me something was broke that I had not spotted (a marginal earth bond value and a brand new IEC lead with a L/N reverse), I tend to find loose screws in about 5% of cables that have not been threadlocked in any given year.
A loose screw in a 125A TP neutral is NOT happymaking!
The computerised tester is good for making pretty stickers that keep the thicker end of the 'elf & safety crowd happy, but I would actually rather people really LOOKED at what they were about to plug in.
Regards, Dan.
dmills
Postby Daniel Davis » Fri Apr 22, 2011 4:50 pm
In my experience working in offices, PAT testing is usually carried out by someone with an automatic machine, but without the exam grades to be a cleaner. No actual physical or electrical examination takes place, and equipment is not tested under load conditions which kinda means that the sticker isn't worth a thing (except perhaps to an insurer).
Why not get an amp tech to look at your valve amps once in a while -- they might actually know what they are doing, although I can't guarantee they'll give you a sticker.
Daniel Davis
Postby dmills » Fri Apr 22, 2011 6:03 pm
Daniel Davis wrote:In my experience working in offices, PAT testing is usually carried out by someone with an automatic machine, but without the exam grades to be a cleaner. No actual physical or electrical examination takes place, and equipment is not tested under load conditions which kinda means that the sticker isn't worth a thing.
A load test is not required as the kit does not have to work, it just has to be safe.
Agree that many of the people doing it are clowns, but without the visual how can the test be said to comply with the ACOP?
That said offices are such low risk environments anyway that the test is mostly pointless in that environment, the folks working in actually dangerous environments tend to do it in house so they know it is right.
We will gloss over the case I heard of where the test reports claimed that everything in a large building was class II (Someone did NOT get paid)!
Regards, Dan.
dmills
Postby Daniel Davis » Fri Apr 22, 2011 6:46 pm
Without a load test you'd have no idea whether some equipment was safe, press a switch and a relay connects your guitar to a potentially lethal voltage - its happened on many a PAT tested valve amp.
Daniel Davis
Postby dmills » Fri Apr 22, 2011 7:10 pm
Nope, press the switch and live shorts to ground taking the fuse or (ideally) RCD out (As long as the ground is present which the earth loop measurement will have established).
Only if the earth is lifted is there a practical risk there and the PAT will find that. Normal practise for the insulation test is that both live and neutral are tied together inside the tester and a high voltage applied between them and ground, thus even a fault downstream of a (single pole) switch will be found.
Note that NO problem on the secondary side of the iron can be found by a PAT tester as it is not looking there.
Regards, Dan.
dmills
Postby Hugh Robjohns » Sat Apr 23, 2011 10:22 am
The Fold Studios wrote:I am self-empployed and run a small recording studio. Am I in trouble if I don't have PAT testing on all my appliances?
Just to reinforce the point, technically no, but you'd be foolish not to have formal PAT or some similar alternative plan in place.
If anyone gets hurt or if you have a claim on your insurance, one of the first things you'll be asked for is evidence of an appropriate and competent system to check and maintain your equipment.
As has been said, the major and most important part of the PAT is the visual inspection which you can easily do yourself. Provided you keep good records of what equipment was tested and when, that should suffice.
Personally, I'd recommend that you take a PAT course at your local college. It only takes a few weeks, it really isn't rocket science, and it doesn't cost that much to do. That way you'll be qualified to test your own gear, and you can also test that of all your mates to earn a few sheckles in the process.... ;)
hugh
Postby zenguitar » Sat Apr 23, 2011 4:06 pm
Hugh Robjohns wrote:Personally, I'd recommend that you take a PAT course at your local college. It only takes a few weeks, it really isn't rocket science, and it doesn't cost that much to do. That way you'll be qualified to test your own gear, and you can also test that of all your mates to earn a few sheckles in the process.... ;)
hugh
I was thinking the same thing recently Hugh. A friend of mine works as a handyman in a local Care Home and they are putting him through the course because it worked out cheaper than getting an electrician in. We did the sums, and at the going rate he could easily make £40 an hour just doing PAT tests.
One course, one machine, a stock of labels, a white van with magnetic promo panels, couple of sweaters with embroidered PAT TESTER logo's and a white lab coat with one of those fancy pen holders in the pocket. Then approach all the Care Homes for 50 miles.
Yogi Berra
Postby planetnine » Sun Apr 24, 2011 10:26 am
zenguitar wrote:
...A friend of mine works as a handyman in a local Care Home and they are putting him through the course because it worked out cheaper than getting an electrician in. We did the sums, and at the going rate he could easily make £40 an hour just doing PAT tests.
£40 at £1.50 per test? That's 26 to 27 items an hour. Not testing properly. And some companies are offering £1 a test, ridiculous.
I test for some charities and a couple of businesses I know/work with, but I wouldn't do it commercially. You earn less than running a studio if you do it properly, and feel less ethical than teaching music technology if you slap stickers on at that rate.
planetnine
Postby planetnine » Sun Apr 24, 2011 11:00 am
please note the bold text Dan, we're actually in agreement here; most problems are visually spotted, but that won't find many earthing and a good many insulation issues. If you set the correct protection (earth) conductor impedance in your PAT tester for the length and conductor x-sect area of the actual cable (rather than use a default setting), you will find strand loss in earth wires and loose earth sockets in extension sockets that would not show up in a visual (yes, I will test all sockets on a six-way dist box).
Damp in some connectors, cables, light fittings isn't alway easy to detect, but with show up in the insulation test (even if it doesn't fail, I look at trends on my outdoor stuff).
You should know from my previous posts on this subject that we concur on most faults being found visually, and it's one of the things many "quantity" companies skimp on. Don't froget that PAT testers can store the results of visual tests, and you can add notes to an asset on them, I rely on this, as well as it telling me where the asset is located (I have over 1000 items of my own to keep track of now, damn festival cabling). The Supernova I got saves me mucking around with various multimeters and current sources, low impedance testers, etc.
The worse bit is writing out the stickers anyway ;)
By testing I did mean the whole visual and connector disassembly inspection too Dan. I feel the biggest point I "gave in" on was the stickers ;)
planetnine
Postby dmills » Sun Apr 24, 2011 12:08 pm
Yea granted, and you do know you can get a sticker printer that plugs into the supernova and even a barcode scanner for it (Ebay quite often).
My point was really for the benefit of those watching, that the IMPORTANT part is the visual.
Regards, Dan.
dmills
Postby zenguitar » Sun Apr 24, 2011 2:47 pm
I agree Nathan, essentially plugging into the test machine, pressing TEST and printing out the sticker. In the Care Home it is 3 or 4 plugs per resident's room, 2 or 3 lamps and a clock radio (no kettles allowed in the rooms) not a lot to visually inspect, but still nowhere near enough time for each.
The course my friend was sent on to do this was one afternoon.
And that highlights the problem with any sort of testing like this. It is perfectly possible to go on a short course to learn to use the machine and be given a quick 'painting by numbers' guide to visual inspection and pass the course with little or no real understanding.
Done properly as described by previous posters, it is a useful practice. But in most cases it is a box ticking exercise to show that they have a Policy and a means of delivering it.
Yogi Berra
Postby planetnine » Mon Apr 25, 2011 9:25 am
I tested the appliances in a local garage where I get my vehicles serviced. Eighty-odd items over seven or eight hours, and I thought that was going some, considering I had to unthread the computer systems and put them back together again :crazy: -most failures involved re-cabling hand-tools.
Previous testing had been done by an established company (from yellow pages). They swore the guy who turned up had not been on site more than an hour, and we found stickers on hard wired alarm systems that would have needed isolating, on low voltage things like laptops (in addition to their PDUs), and then the number of stickers and asset numbers we found did not correlate with the amount they'd been charged.
This seems to be quite common, too. I can't do a bodge-job, it's not me. I wouldn't make much money PAT testing commercially.
Dan -I've considered the bar-code reader. If it stores the asset number and the item's test code, then that could be good for repeat stuff. Means a lot of mucking about with printing labels though, or an expensive portable printer with expensive proprietary labels.
My, haven't we taken this on a tangent?
planetnine
Postby geefunk » Thu Apr 28, 2011 2:49 pm
I neeed some advice on this too. I'm in a school, and we've just had an annual PAT test, and 8 of my brand new, still in the box power extension reels were failed because they have 10amp cable (13amp plug/fuse), and it is thinner than 13amp cable, so illegal?
We already had one in the school, and it was passed by the company last year, but a different company have failed it this year. What is the situation?
geefunk
I honestly think you ought to sit down calmly, take a stress pill and think things over
Twitter
Next